Discuss Advice, if any on installing a shower please. in the UK Electrical Forum area at ElectriciansForums.net

N

Newinthegame

Hi there Guys,
I got good feedback on my last post and being a newbie sparks wanted some guidance on this one please.
Customer requires a new shower to be fitted. 10.5KW
There is an existing 6mm t+e in the loft, but i am going to upgrade this to 10mm and connect into the contactum DB....rcd side via a 50 amp breaker.
The main supply to the DB is a 16mm t+e which comes from a very old MEM switchfuse which has....i think a 60a fusewire attached.
Would it be wise to change this switch to a 80/100 amp isolator. RCD aswell because it is TT system. Concerned that this may blow under the extra load!!!
Does this sound ok? Any advice would be great.:lightbulb:
 
If cant quite work out if the Contactum DB is what you are fitting or the original?

If it is original you don't need the old MEM switch fuse, just upgrade tails and earthing if required.

If it not original, 25mm tails into Henley block and split tails into MEM switch fuse and new Contactum DB.
 
The contactum DB is the original DB in the house which is on the first floor.
The incoming supply(T-T) comes into a seperate outbuilding about 4/5 metres from the contactum DB. The outbuilding is where the MEM switchfuse is and it is this that supplies the DB via a 16mm T+E. My concern is that with the additional load from the shower the fuse may blow because i think it is rated at 60 amp. Do i change the switchfuse because of the distance to the DB? And its T-T so it should now be an RCD?
 
The contactum DB is the original DB in the house which is on the first floor.
The incoming supply(T-T) comes into a seperate outbuilding about 4/5 metres from the contactum DB. The outbuilding is where the MEM switchfuse is and it is this that supplies the DB via a 16mm T+E. My concern is that with the additional load from the shower the fuse may blow because i think it is rated at 60 amp. Do i change the switchfuse because of the distance to the DB? NO

And its T-T so it should now be an RCD? YES

What other loads / circuits are on the house DB ?
 
Standard stuff. 1 x cooker, 1 x ring main, 2 x lighting, 2 x radials, 1 x CH boiler.
Gettin a bit confused though. Dont wanna run the risk of leaving in the mem switchfuse and the fuse blows when the shower is on. Then there would be no supply to the DB. So if i change it then i must replace with a DP RCD 80a 30Ma?? this way it then protects the 16mm t+e going to the DB right?
 
The problem isnt whether to replace the MEM fuse for a bigger one , but whether the 16mm T&E submains to the house is upto the job of suppyling extra loads.
Unfortunatley i'd say not when you consider the existing circuits already in use.

How is the submains installed ?
clipped direct , buried in ground , in conduit , suspended overhead ?
 
Last edited by a moderator:
So if i change it then i must replace with a DP RCD 80a 30Ma??

tails would only require RCD protection if buried <50mm deep in walls.
 

Reply to Advice, if any on installing a shower please. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi All I'm in the process of getting quotes to get an EV Charger installed, and hopefully at the same time power to 14 residents garages. As it...
Replies
2
Views
2K
Hi, I need some advice on a garden supply project. An existing small garden shed is being replaced which had a supply to it for a light and two...
Replies
12
Views
5K
Hi all im needing some advice on installing a hot tub, the spec of the hot tub says it requires a 32amp supply, My plan is to run 6mm t+e from a...
Replies
1
Views
718
I was asked a question today if it would be possible to use an existing cable that was previously installed to supply a shower which has been...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock