exactly what i was getting at, the earth is only live during fault conditions

That isn't true. There will be a certain amount of legitimate earth leakage from appliances. Don't forget that there is functional earthing as well as protective earthing.

And as pointed out, under fault conditions there could be a significant current flowing.
 
When the SWA is used as the CPC outside the box, and a length of 6491X lugged onto the banjo bolt serves on the inside, the low resistance path connecting them together is via the brass of the banjo and the bolt, rather than through the enamelled steel enclosure which might make relatively poor contact and is of lower conductivity compared to the brass. So in the event of a fault the banjo bolt carries most of the fault current through a separate hole.

What's the solution? Single hole banjo? Moebius bolt that goes through both holes and back to where it came from? Slot the banjo bolt hole across to the gland entry? :)
 
When the SWA is used as the CPC outside the box, and a length of 6491X lugged onto the banjo bolt serves on the inside, the low resistance path connecting them together is via the brass of the banjo and the bolt, rather than through the enamelled steel enclosure which might make relatively poor contact and is of lower conductivity compared to the brass. So in the event of a fault the banjo bolt carries most of the fault current through a separate hole.

What's the solution? Single hole banjo? Moebius bolt that goes through both holes and back to where it came from? Slot the banjo bolt hole across to the gland entry? :)

Do like I do and put the banjo inside?
Not an issue really outside or inside, the contact area is greater inside, than out.
Don't drill the enclosure, why would you?
 
That isn't true. There will be a certain amount of legitimate earth leakage from appliances. Don't forget that there is functional earthing as well as protective earthing.

And as pointed out, under fault conditions there could be a significant current flowing.

There is no functional earthing in a domestic installation.
 
Indeed, functional earthing is where most legitimate leakage current comes from. Not that it has anything much to do with eddy currents - they start being a problem with hundreds of amps, not a few mA.
 
Indeed, functional earthing is where most legitimate leakage current comes from. Not that it has anything much to do with eddy currents - they start being a problem with hundreds of amps, not a few mA.

Completely agree. Just pointing out that it isn't correct to state that there can be no current on the Earthing Conductor without a fault current.
 
Indeed, functional earthing is where most legitimate leakage current comes from. Not that it has anything much to do with eddy currents - they start being a problem with hundreds of amps, not a few mA.
thats my point, you wouldn't get 100amps flowing on the earth in a domestic property

in commercial/industrial yes it is something to consider because of the size of the supply etc.

now i will follow the reg but im just saying in my opinion its belt and braces with reguards to the earth

if people have safely put the earth in the board for the last 100+ years i doubt it is cause for concern
 
Last edited:
Maybe momentarily under extreme fault conditions but unlikely.
a fault current that high would melt the copper where the fault is located and clear it before the eddy currents would start to work on the earth

i doubt 6ka fault current would be enough to instantly cause noticble affects on the install before it trips the breaker
 
Last edited:
You chose to bump this thread Dan!!!
Could get interesting if the same characters are still around :)
 
New posts

Reply to Advice on regulation 521.5.1 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all. I am installing some metal trunking vertically in a meter cupboard to contain all the meter tails for an apartment block. I have 5 sets...
Replies
1
Views
655
I’ve always been alright with the knockouts provided for Fusebox consumer units but I’ve got a job coming up where I don’t want to use the large...
Replies
24
Views
1K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
844
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
612
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
207

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock