I’m after some clarification please. I have wall mounted the TV and want to install a double socket behind it. I planned on taking a spur from the socket as shown in the photo (bottom right) running the 2.5mm T&E cable in the safe zone to behind the TV. The cable run is 2.4metres and the new spur socket will power the TV and a Sky mini box. The existing socket is not a spur as it has two cables. The more I researched this the more I got confused. Am I permitted to do this within regulations?
 
Last edited:
Morning mate,Just because it has 2 cables doesn’t mean it’s a rfc it could also be a radial circuit, assuming it is a rfc and you have rcd protection in place then you can spur from there....safe isolation is paramount and if you are not that sure a local spark is not going to change to much for that mate it wouldn’t take long.....has someone changed a double to a single at some point?
 
Morning mate,Just because it has 2 cables doesn’t mean it’s a rfc it could also be a radial circuit, assuming it is a rfc and you have rcd protection in place then you can spur from there....safe isolation is paramount and if you are not that sure a local spark is not going to change to much for that mate it wouldn’t take long.....has someone changed a double to a single at some point?
We moved into the house 20 yrs ago as a new build. That single socket was the original socket and I think my father in law had spurred from this and put a double right next to it as we had a different room layout. I removed this a few weeks ago when we had a new internal wall put up.
 

Reply to Advice on spur socket from ring main in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
681
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
575
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
698
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock