Morning all

After some advice please, thank you.

I've installed a 40amp submain for a garage supply, wired in SWA and have exported the PME (tin hat on)

30ma RCD in house, main switch in garage cu.

All good until customer tells me that they're having a a car charger installed.

New regs stipulate this must be on TT system.

So off we are today to change it all over. Move RCD to garage and bang a rod in.

One question which I think I know the answer to, is that the nice newly installed metal garage cu now has to be changed to plastic? Am I correct.

Thanks Sy
 
Morning all

After some advice please, thank you.

I've installed a 40amp submain for a garage supply, wired in SWA and have exported the PME (tin hat on)

30ma RCD in house, main switch in garage cu.

All good until customer tells me that they're having a a car charger installed.

New regs stipulate this must be on TT system.

So off we are today to change it all over. Move RCD to garage and bang a rod in.

One question which I think I know the answer to, is that the nice newly installed metal garage cu now has to be changed to plastic? Am I correct.

Thanks Sy

Reg number???
 
Morning all

After some advice please, thank you.

I've installed a 40amp submain for a garage supply, wired in SWA and have exported the PME (tin hat on)

30ma RCD in house, main switch in garage cu.

All good until customer tells me that they're having a a car charger installed.

New regs stipulate this must be on TT system.

So off we are today to change it all over. Move RCD to garage and bang a rod in.

One question which I think I know the answer to, is that the nice newly installed metal garage cu now has to be changed to plastic? Am I correct.

Thanks Sy

I would suggest you red BS7671 Section 722 Sy and not listen to your customer, who obviously has been miss informed.
 
Here's you go : 722.411.4.1

And haven't had to install any TT for a very long time, hence the question.

Cheers Sy



Cheers Sy

if you read on it says "The requirements of this regulation need not be applied for the charging point at a dwelling...."

So is the charging point outside? if so move inside the garage!
 
I have only ever had one instance where a customer insisted that something be TT'd.
It was for a laser cutting machine from China.
The cutter wasn't working correctly, and the Chinese were worried that the earth wasn't up to scratch.
Eventually they got their landlord to drill through the slab (and any DPC if installed) and install a rod, which I then connected to the machine.
Eventually the Chinese sent someone over to re-program the cutter.
 
TT'd it in the end....

Keeps customer happy otherwise they wouldn't have fitted his charger and learnt something for just in case next time.

Apparently BMW sub the job out to Schneider, who sub to a local firm.
 

Reply to Advice please... TT metal/ plastic cu in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock