Discuss Advice required on behalf of elderley mother in the UK Electrical Forum area at ElectriciansForums.net

Archangel

DIY
Reaction score
2
My elderley dad recently passed away leaving my elderley mother to update the house theyve shared for decades in the Birmingham area. She thought she was doing the right thing by speaking to a long retired electrician if he knew of anyone who could install a few new plugs she needed for a new fireplace, and to look at the wiring in general which was very old and needed updating badly. The retired electrician said he knew a few guys who he thought were ok and they visited my mother.
The guys have ended up fitting a new CU fuse box to the electrical meter, changed various bits of wiring to various rooms by fitting double sockets to the surface of internal walls, leaving electrical wiring trailing down the walls unsheaved (bottom floor), but with plastic conduit over in upstairs rooms. Its been done very untidily and messily, and with no regard to looking nice or hidden as you would in a house.
To rub salt into the wounds theyre not forthcoming with a receipt for 732.00 work or a certificate (I presume Part P?) which guarantees their work? They said they will arrange the certificate if mom pays them a further 100.00 so they can arrange someone to do this?
I dont know much about electrical work, but all i can get our mom to find out now is that they may not be registered electricians but friends of friends who have done cash in hand work. DO WE HAVE ANY RIGHT TO DEMAND A FREE PART P CERTIFICATE ETC?
 
Attached pics as requested

20191006_161919.jpg 20191006_161928.jpg 20191006_161847.jpg 20191006_161850.jpg 20191006_161853.jpg 20191006_161902.jpg 20191006_161905.jpg 20191006_161915.jpg
[automerge]1570478450[/automerge]
Sounds like a right couple of cowboys

Board change pictures would make interesting viewing
Will try post them tomorrow showing the board
 
Those pictures are not a great indicator of someone taking pride in there work, in regards to certification by any chance did you/your mum get any form of written quotation or check there credentials?
 
although that min trunking is a bit rough, it could just be that the guys did not want to cause redecoration due to chasing out and an elderly lady. 2 sides to every story.
 
I agree min trunking is not uncommon when adding additional sockets in domestic, especially running down door frames or in corners, but they could of spent a bit of time finishing it off, unfortunately this sounds like a mate of a mate from the pub
[automerge]1570480376[/automerge]
Agree with dusty above, if safe to do so and comfortable doing it,some pics of the DB would be good.
 
Agree with tel. Sometimes surface trunking is the only option open.

However, it does sound a little dodgy. It may be a lesson learned there about who you get to do work in the house in the future
 
There should be an EIC (electrical installation certificate) and the work is notifiable to Building Control. With regards to the aesthetics, was the original quote to supply surface mounted trunking, or to conceal (chase in) cables, mindful that wallpaper etc. would be ruined and areas woudl require making good.
 
although that min trunking is a bit rough, it could just be that the guys did not want to cause redecoration due to chasing out and an elderly lady. 2 sides to every story.
Agreed.....but that '£100 extra for getting someone to certificate' really sets the bells ringing for me.
It'll be interesting to see the replacement CU.
…...I detest those who take advantage of, or fleece, the elderly.....lowest of the low.
 
How was the work payed for, please don’t say cash
Cash in hand!!
[automerge]1570509694[/automerge]
I agree and am grateful for everyone's comments above.Mom didn't realise what she was doing, didn't get a written quote and paid cash in hand. The certificate should be given by them free of charge whether or not they are registered. Am I right in saying this? What should we do now? Speak to building control or employ a certified electrician to check the work at more cost and provide certification? Appreciate your views guys.
 
Last edited:
I doubt building control will show any interest. As said it’s not the greatest, but not lashed in, so doubt trading standard would be either. Think wisely; LBC could offer to have your new CU tested, a Regularisation Certificate, my LBC charges £400 + vat for that process.

The BS wiring regs, gives guidance that electrical certification should be provided on completion of works. Ask for that first. As said pics of your CU, might be a gauge. £100 extra for testing & compliance certificate, seems a bit naughty, but might be a way out of this dilemma, dependant on the ‘tester’ neutrality.

Pics first.
 
Do you know the names of the guys/company that carried out the work? Sounds very dodgy when they say they can arrange a certificate for extra £100 which suggests no testing has been done at all. Would they be susceptible to a few negative reviews? Go back to the retired spark that recommended them?
 
Do you know the names of the guys/company that carried out the work? Sounds very dodgy when they say they can arrange a certificate for extra £100 which suggests no testing has been done at all. Would they be susceptible to a few negative reviews? Go back to the retired spark that recommended them?
He could be one of them Alan!! Or at least involved with them.
 
would like to see pic. of inside that CU if you can safely remove the cover with main switch off
 
The fact that both the 'general' socket circuits and both lighting circuits are on the same side of the RCD is a definite red flag for me. Following on, both the 'general' socket circuits have what appear to be 32A ring finals, where as the kitchen sockets - which will arguably have the biggest load - have what looks like a 16A radial. Very strange installation design.

EDIT - My mistake, I misread 'Shower' for 'Sockets' on circuit two. Even so, the fact an electric shower is on a 32A circuit breaker might be even more concerning. Would definitely get it checked out by an independent electrician.
 
I don't think this is wise @telectrix

The OP has said in their first post they don't know much about electrics. And then to ask them to pull something apart to look (I know it might be 1 screw - but still).

I think we've exhausted what we can actually help with. The rest is just curiosity? - Not sure.
 
OK, Dan. maybe jumped the gun there. we don't know exactly the OP's competence level and safety awareness. OP does however have a mate of his dad, who is a retired spark. perhaps he'swilling to advise in an on site capacity. btw, while you're on, can you get my like etc. button back. it's missing. i can't leave reactions. :) .
 
Last edited:
OK, Dan. maybe jumped the gun there. we don't know exactly the OP's competence level and safety awareness. btw, while you're on, can you get my like etc. button back. it's missing. i can't leave reactions. :) .
I refer you to his very first post.
I dont know much about electrical work
:)

Be careful telling people pull off electrical covers to mains. That's all I'm saying matey.

For all we know he'd be fine. But for the one in 100 that aren't, just by pure numbers, we're going to end up telling them to do it too.
 
OK, Dan. point taken. on re-reading OP, i seem to have confused with a similar post where the OP knew a retired MEB spark. apologies to OP. and thanks to Dan for finding my like button. :):):)
 
Before proceeding anywhere @Archangel, ask for your Electrical Installation Certificate. It part of the installation, as I alluded to in #16.

The replacement CU should be notified to your LBC, unfortunately and ultimately its the householders responsibility, to ensure that Building Regulations are complied with.

At what stage, did you become aware of this matter? £732 for a CU replacement and a few sockets, is not fraudulently steep, but asking for another £100 is starting to sound to me now, as somewhat 'suspicious' irregular.
 
My post seems to have disappeared....

Anyway

No point getting the original people back who did a bad job , they will only fudge it

All I would do now is get a EICR done and see what that throws up
 
Once again I'm grateful for everyone's replies.
In reply to clarify a few points...I dont live with my mother so didn't find out about all the work done until after the event..they charged her £735 for rewiring parts if the house and fitting new double plug sockets on the outside of internals walls...whilst doing so they've either left cables dangling from the socket to the floorboards or fitted plastic trucking over them...having quizzed my mother further it WAS all discussed with her but she didn't like the result afterwards..nothing has ever been written all work verbally agreed...no she didn't check them out prior to using them she replied on one of dads old work mates to recommend them...the electric meter was/is ancient so they've fitted a new fuse board/board as per the pictures...they havent been seen since and keep telling mother the receipt will be put in the post...they refuse to provide the certificate for their work on the basis they need to get another bloke to do the checking and provide the certificate at a further £100 cost....this is where mother is at. I've given her the advice as seen above and advised her to get another qualified electrician in to do the checks or she is to consider trading standards/LABC herself (with family help). If anyone has any other advice please feel free and I'm grateful.
 
As an inspector and tester I have to agree the work looks untidy and could have been finished to a much better standard, trunking is commonly used where tracking is not an option and I think this is probally one of thoes cases, with regards to a new CCU this would require an EIC as per the regulations (644.1) nothing less and you should not be charged extra for this, the other issue I have is the 16A mcb for the kitchen sockets this is where the highest load is in any house and should have been investigated in to making this a ring final circuit, but this should have been discussed with the client and I suspect the lady would have agreeded to have this done had she been told as she had concerns over the installation in the first place, the lighting circuits should have been split to provide some discrimination and not both on the same RCD.
Bottom line its a shabby job and no self respecting spark would be happy to put their name to this.
 

Reply to Advice required on behalf of elderley mother in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
827
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
612
I'm moving a socket installed on a lighting circuit (installed by previous owner who was a professional electrician so I assume he knew what he...
Replies
7
Views
1K
Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock