Discuss All neutrals connected at one point - two rcds. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Hi guys.
Fuseboard looks fine, but all neutrals are connected at one point outside the fuseboard. That way both rcds trip on fault on any of the circuirs.How would yiu code that?
P.s. also no glanding and cables rubbing on the sharp edges of CU?
Thanks
 

Attachments

  • 20221020_173520.jpg
    324.3 KB · Views: 48
  • 20221020_173544.jpg
    542.9 KB · Views: 48
  • 20221020_163909.jpg
    150.9 KB · Views: 49
FI for the neutral conductors and RCD’s

C2’s for the lack of mechanical protection, IP rating and single insulated cables out side of an enclosure.
 
Hi guys.
Fuseboard looks fine, but all neutrals are connected at one point outside the fuseboard. That way both rcds trip on fault on any of the circuirs.How would yiu code that?
P.s. also no glanding and cables rubbing on the sharp edges of CU?
Thanks
I am surprised that they dont trip whenever anything is used, let alone a fault.
 
Some unqualified 'electrician' have just installed the board a week ago without certificate, and the landlord asks for EICR, so he can rent the property. The flat is still completely empty.

There's no way that was done by an electrician of any kind.
I'd bet the landlord did it themselves.
 

Reply to All neutrals connected at one point - two rcds. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
458
Hello sparkles, I have a question in relation to sequencing the RCDs and MCBs in the CU. I called an electrician to come to my house and upgrade...
Replies
7
Views
1K
I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
735
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock