Evening all. Just getting my fireproof trousers on ready for being shot down in flames......I try not to post too many questions on here as it highlights how little I know, but I'm doing my best to learn from others and my own mistakes and sometimes there's no-one else to ask. So here goes:
I've been out to a house today which is going to be rented out - they wanted an additional socket put in before tenants move in. PME supply with 16mm tails, 10mm earth and a 16th Edition board with BS3781 MCBs and no RCD.
My question is around what are 'Requirements' and what are merely 'nice to do' actions in terms of work.
From conversations I've had with more experienced electricians, I've been led to believe that by making an addition to the circuit (i.e. spur for the extra socket) I would need to ensure that the installation is brought up to current standards.
So, in this case:
Upgrade 16mm to 25mm tails?
Upgrade 10mm to 16mm earth?
Install either an RCD upfront, an RCBO in that particular circuit, replace the whole board or use an RCD socket outlet?
Oh, and the tails were a lot longer than 3m, so a switchfuse at the cut-out too?
Obviously, this is significantly more work than the customer was expecting!!
Am I way off the mark here, or are all these actions necessary before I can put an extra socket in?!?
Thanks for your time (and patience)
I've been out to a house today which is going to be rented out - they wanted an additional socket put in before tenants move in. PME supply with 16mm tails, 10mm earth and a 16th Edition board with BS3781 MCBs and no RCD.
My question is around what are 'Requirements' and what are merely 'nice to do' actions in terms of work.
From conversations I've had with more experienced electricians, I've been led to believe that by making an addition to the circuit (i.e. spur for the extra socket) I would need to ensure that the installation is brought up to current standards.
So, in this case:
Upgrade 16mm to 25mm tails?
Upgrade 10mm to 16mm earth?
Install either an RCD upfront, an RCBO in that particular circuit, replace the whole board or use an RCD socket outlet?
Oh, and the tails were a lot longer than 3m, so a switchfuse at the cut-out too?
Obviously, this is significantly more work than the customer was expecting!!
Am I way off the mark here, or are all these actions necessary before I can put an extra socket in?!?
Thanks for your time (and patience)