I know this because its what we use when we wire smoke circuits.
a quick google says an average CO Detector uses 1 amp ish.
1.5mm cable is rated for 14.5a in my blue book nice bit of headroom there
since that CO that uses 1amp ish is no where near that its acceptable to use a 6amp breaker
finally its a domestic setting so B- type is what we use, C is for commercial and D is for industrial
A CO detector will use nowhere near 1Amp, that would be an awful lot of power to operate a small amount of electronics.
If its less than 1A why not use a 1A MCB rather than a 6A?
No, B, C, D does not denote domestic, commercial, industrial, it denotes the tripping curve or how much inrush the MCB can tolerate be for tripping.