Got my AM2 Monday, just wondered if anyone could give me any advice if they have taken it before or things to be wary of.

Could someone please explain to me using fly earth leads, when to use and when to jot? Might seem simple but my college have basically put me for the AM2 with barely any help from them
 
Do you have to use fly leads connected to a banjo when using SWA and SY cable. Also when doing the PFC tests do you test each phase to earth and double the highest reading and record that as you ipf and just record the PSCC (phase to neutral??) on the back of the test sheet

If the sheath or screen is being used as protective conductor then yes, you need to banjo and fly lead to the earth terminals.

Be careful with your terminology. Measure PEFC (L-E) and PSSC (L-N), the highest of the two values becomes the PFC. Record this value if only Single Phase is present. Double it and then record value if Three Phase is present.
 
Another question, on my test results I have 2 circuits that are 3 phase do I put e.g motor circuit L1 then all the results for that phase then underneath motor circuit L2 then all the results etc or do I put motor circuit and take the highest reading off all of the results I get for each phases and use that?
 
Got my AM2 Monday, just wondered if anyone could give me any advice if they have taken it before or things to be wary of.

Could someone please explain to me using fly earth leads, when to use and when to jot? Might seem simple but my college have basically put me for the AM2 with barely any help from them

Hello Anthony,

Just interested in how you got on in the AM2 test?
 
If the sheath or screen is being used as protective conductor then yes, you need to banjo and fly lead to the earth terminals.

Be careful with your terminology. Measure PEFC (L-E) and PSSC (L-N), the highest of the two values becomes the PFC. Record this value if only Single Phase is present. Double it and then record value if Three Phase is present.
Phase to phase is the worst case on a 3 phase supply this should be measured then doubled and recorded
 

Reply to AM2 help for Monday please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

This might come across as a really daft question to people who work with cable tray quite often but as part of my AM2, I am to clip FP200 to the...
Replies
31
Views
2K
I have my AM2 coming up next week but something is puzzling me and I’m hoping someone can help me out. So there is some SY cable coming out of...
Replies
11
Views
2K
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
703
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi, I’m just looking for some advice/ someone to point me in the right direction please. Basically I worked as an electrician for 5ish years...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock