Discuss AM2 Questions Testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Sorry that you have had a temporary delay in passing. Do not give up yet.
Continuity of ring final circuit conductors:
Isolate power supply and prove dead, remove the conductors and measure the end to end resistance of each core giving you r1, rn and r2, check that the resistances are consistent i.e within r1 and rn nearly equal and r2 either equal with singles or 1.67 times higher with twin and earth, note down these results and add them to the schedule of test results for that circuit.
Calculate your expected values (r1+rn)/4 and (r1+r2)/4 for the figure eight measurements and note this down.
cross connect L and N and measure the resistance at each point of use in the circuit, make sure they are all the same and match (within 0.05Ω) the calculated value note down the measured value.
repeat the above for the L and cpc cross connection.
write down the measured value obtained in this last set of measurements as the R1+R2 of the circuit on the schedule of test results.
reinstate the circuit removing all cross connections.
move on to insulation resistance testing.

Earth fault loop impedance:
depends on whether it is external or for a circuit.
measurement of external EFLI should be done with the board off , main switch open and the main earth removed; measured and recorded and then the main earth reconnected. All dead tests should have been completed and recorded and recognised as complaint prior to starting live testing.
measurement for a circuit should be done only after all dead tests for all circuits are completed and correct. The main earth must be connected and also all bonding
conductors. The result should be recorded.

Even though I have been very brief, if you have done all that then you should have been OK.
 

Reply to AM2 Questions Testing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
740
I have my AM2 coming up next week but something is puzzling me and I’m hoping someone can help me out. So there is some SY cable coming out of...
Replies
11
Views
2K
Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Replies
1
Views
914
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hey all, First post but have read up a lot over the last few months as I have been prepping for my AM2s which I sat last week and thought I done...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock