Search for tools and product advice,

Discuss AM2 Questions in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Reaction score
7
I have my AM2 booked soon and had a few questions

What multifunction tester is provided or does it vary between am2 centres?

I am doing preparation course online so i am just wondering if the installation is going to be the same layout or similar

Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
 
I have my AM2 booked soon and had a few questions

What multifunction tester is provided or does it vary between am2 centres?

I am doing preparation course online so i am just wondering if the installation is going to be the same layout or similar

Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
Think they advise you to take your own they did when I did 2391
 
There's yer answer I guess Mate good luck
Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
 
Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
Should have been covered during your course tuition, if you attended all of the lectures, asking questions during the course is best, not leaving it till the last minute on an internet forum.
Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
Can't help you mate sorry the AM2 was a futurism when I was an Apprentice Electrician, it was all UEI and C and Gs
 
Should have been covered during your course tuition, if you attended all of the lectures, asking questions during the course is best, not leaving it till the last minute on an internet forum.

Can't help you mate sorry the AM2 was a futurism when I was an Apprentice Electrician, it was all UEI and C and Gs
wasn't it in Latin back then? i remember doing latin in secondary school. wondered why as all the electrical books in the library were in english.
 
wasn't it in Latin back then? i remember doing latin in secondary school. wondered why as all the electrical books in the library were in english.
Dunno Tel I took Maths, English, Social studies and in the final three or four years it was C n Gs probably something to do with non Grammar School Lads getting up to speed, still got all my certs including UEI could go and get them but it's cold and wet here, I'll get them tomoz OK?
 
When I did my AM2, the MFT was a Kewtech... didn't like it at all.

On the fault finding section, the faults are picked at random... they set them up and give you the fault details. The detail will include the affected circuit, so it's not like 'my board is tripping' and you have to look at everything.
 
I have my AM2 booked soon and had a few questions

What multifunction tester is provided or does it vary between am2 centres?

I am doing preparation course online so i am just wondering if the installation is going to be the same layout or similar

Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
you are given at least 3 major brand multifunction testers.
all the AM2 installations are identical.
the fault finding is done as follows:

1 the assessor is told what fault to switch on, you cannot see the switch.
2. you are given a description of a fault ie: the breaker trips when the central heating is called for. This gives you the area to look in ie the solar thermal system.
you will be given a total of 7 faults in total which you are supposed to find in the order you are given. Your answer should identify the fault, where it is and what you would do to rectify it. the assessor does not pick the faults as he is given them by NET.
the fault finding is done after you have carried out safe isolation as it is done dead. good luck
 
I have my AM2 booked soon and had a few questions

What multifunction tester is provided or does it vary between am2 centres?

I am doing preparation course online so i am just wondering if the installation is going to be the same layout or similar

Im covering all sections of fault finding and testing on the AM2 prep
on the AM2 does the assessor make sure you cover all the sections or are they chosen at random?
Do they create a fault on one or two circuits ? or do i need to run through all the circuits with a multi meter explaining how to find short or open circuits ?
you are gien a choice of
 
I was also curious about what MFT they would provide it is definitely reassuring knowing you get a selection rather than turning up and "here is your tester" only to be something totally alien to you.

Ed Evans - would you first tackle the faults making sure you have continuity from DB to the said area on all conductors/cpc & then if yes move on to using other testing methods if you cannot find the fault e.g I.R testing etc
 
@Ed Evans ,

Test centres are not obliged to provide a choice of manufacturers when it comes to test equipment. They are only obliged to provide a certain number of devices for a given number of bays. I had no choice... if I had a choice between say Megger and Kewtech or Fluke and Kewtech... I would have opted to use the Megger or Fluke.

The AM2 test centre specification only states the equipment they must provide... it does not stipulate candidates must have a choice.

https://www.netservices.org.uk/wp-c...M2-S-Assessment-Centre-Specification-v3.0.pdf
 
I was also curious about what MFT they would provide it is definitely reassuring knowing you get a selection rather than turning up and "here is your tester" only to be something totally alien to you.

Ed Evans - would you first tackle the faults making sure you have continuity from DB to the said area on all conductors/cpc & then if yes move on to using other testing methods if you cannot find the fault e.g I.R testing etc

Don't expect a choice of test equipment. See my post above and read the test centre specification document. It tells you what centres are obliged to provide. Don't expect it to be the best quality either, the tool kits get alot of abuse.

As for the fault finding... I would go straight for a test that is the most appropriate for the fault. You can assume everything else is perfect apart from the fault you are trying to find.
 
Ah I see, sorry I misread, thanks for the information sparky its always nice to learn as much info as possible.
I guess when the time comes I would enquire about what mft they use not keen on the kewtech like yourself
I definitely need to get some practice in the fault finding department before even booking the am2.
 
Hi mate,
The training center provides you will all the tools and test equipment you need. From what I can remember when I did mine there was a selection of testers and I was asked to preform safe isolation and had to select the tester and a proving unit.
Usually the examiner will put faults on the test rig and you have to find them.
when you do your installation he dismantles. Your accessories/ wiring and checks your connections to see if there’s any conductor showing.
but if your the type of guy asking questions on this forum before you do it you’ll be fine.
good luck
 
I was also curious about what MFT they would provide it is definitely reassuring knowing you get a selection rather than turning up and "here is your tester" only to be something totally alien to you.

Ed Evans - would you first tackle the faults making sure you have continuity from DB to the said area on all conductors/cpc & then if yes move on to using other testing methods if you cannot find the fault e.g I.R testing etc
you are given normally a fluke, megger and possibly a metrel multifunction tester. Do NOT use these for safe isolation.

Do not start with the same continuity tests as if it possibly is taking out the cb then continuity would show as ok, wouldn't it?

read the descriptor, step, back and think what the cause could be. You will have plenty of time doing this as you will not be wasting time looking for a test result that would not prove anything.

for example: the cat 5 (bt) fault one of them is 2 lines crossed over. S, continuity red to red ok
blue to blue open. But that is not the fault because if the blue at one end went to the green it would show open because the blue is going to the green. but it is not open it is crossed.
 
you are given at least 3 major brand multifunction testers.
all the AM2 installations are identical.
the fault finding is done as follows:

1 the assessor is told what fault to switch on, you cannot see the switch.
2. you are given a description of a fault ie: the breaker trips when the central heating is called for. This gives you the area to look in ie the solar thermal system.
you will be given a total of 7 faults in total which you are supposed to find in the order you are given. Your answer should identify the fault, where it is and what you would do to rectify it. the assessor does not pick the faults as he is given them by NET.
the fault finding is done after you have carried out safe isolation as it is done dead. good luck
Thank you for this really helpful
 
you are given normally a fluke, megger and possibly a metrel multifunction tester. Do NOT use these for safe isolation.

Do not start with the same continuity tests as if it possibly is taking out the cb then continuity would show as ok, wouldn't it?

read the descriptor, step, back and think what the cause could be. You will have plenty of time doing this as you will not be wasting time looking for a test result that would not prove anything.

for example: the cat 5 (bt) fault one of them is 2 lines crossed over. S, continuity red to red ok
blue to blue open. But that is not the fault because if the blue at one end went to the green it would show open because the blue is going to the green. but it is not open it is crossed.
Thanks mate
Also when i go through all the different tests in the inspection and testing section I will connect the cpc and neutral leads together because it is a 3 phase board and i will be doing 3 phase tests for example ze and pfc tests , is that correct?
thanks
 

Reply to AM2 Questions in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
440
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
872
Hi Guys I am currently on the NVQ 2357 on my way for the AM2 and get fully qualified, at the moment i am doing private jobs, on the NVQ 2357 they...
Replies
1
Views
497
Hello everyone and nice to meet you all! I have question, I'm interested in doing my am2 test,the problem is working frew various agencies you...
Replies
0
Views
767
Hey all, First post but have read up a lot over the last few months as I have been prepping for my AM2s which I sat last week and thought I done...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock