Discuss Am2, what size cable for the heating system in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi everyone I have my am2 resit coming up and was wondering what size cable do you use from the wiring centre, to the programmer, and what size cable is used from the wiring centre to the thermostat. I thought it was 1.5, but wasn't sure.

Any answers will be much appreciated, thanks a lot.
 
The size of the cable is always dictated by the OCPD (fuse or mcb) value and its installation method (as in can it dissipate heat ) , in central heating you need to make sure it has enough cores for the purpose , ie a minimum of 4 core for room stat ( N , L , SL , CPC)
 
The size of the cable is always dictated by the OCPD (fuse or mcb) value and its installation method (as in can it dissipate heat ) , in central heating you need to make sure it has enough cores for the purpose , ie a minimum of 4 core for room stat ( N , L , SL , CPC)
Okay thank u mate, the spur has a 3 amp fuse. Is there a calculation I can use to dicate the cable size?
 
The size of the cable is always dictated by the OCPD (fuse or mcb) value and its installation method (as in can it dissipate heat ) , in central heating you need to make sure it has enough cores for the purpose , ie a minimum of 4 core for room stat ( N , L , SL , CPC)
i would say that the cable size is determined by the load, and then the OCPD is determined by the cable size. beg to differ.
 
Okay thank u mate, the spur has a 3 amp fuse. Is there a calculation I can use to dicate the cable size?
it's a 3A fuse because the load is<3A. then the cable size can be anything that is rated at >3A according to the installation method. therefore even 0.5mm would usually suffice, but 0.75mm is the norm as it's usually flex.
 
it's a 3A fuse because the load is<3A. then the cable size can be anything that is rated at >3A according to the installation method. therefore even 0.5mm would usually suffice, but 0.75mm is the norm as it's usually flex.
Okay that's great cheers mate, what about the single core cables for the programmer and thermostat, what would the size be for them?
 
In the am2 all of the cables are supplied and a drawing is provided, I'm not 100% sure, but I think the drawing dictates what size of cable to use/what type and each cable is used once, its more being able to follow the drawing more than anything. I don't think any calculations are required on the day.
 
In the am2 all of the cables are supplied and a drawing is provided, I'm not 100% sure, but I think the drawing dictates what size of cable to use/what type and each cable is used once, its more being able to follow the drawing more than anything. I don't think any calculations are required on the day.
Thanks mate, that's reassuring appreciate it.
 
Hi everyone I have my am2 resit coming up and was wondering what size cable do you use from the wiring centre, to the programmer, and what size cable is used from the wiring centre to the thermostat. I thought it was 1.5, but wasn't sure.

Any answers will be much appreciated, thanks a lot.
The cable size is dictated on the installation design drawing. If you are unsure you are encouraged to confirm with the assessor, you won't fail for asking as they would rather you do that than get it wrong.
 

Reply to Am2, what size cable for the heating system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
874
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
995
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
440
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
568

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock