Discuss AMD 3 DB on a TT system in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
Hello Guys

being a Londoner i have not had a great deal of experience with TT systems in a domestic setting.

The existing installation is in the basement, the existing earth rod is by the DB and sticking out of the ground, not inspection pit is that quite bad?
I was thinking of changing the rod and installing a pit, how long should the rod normally be to make sure i get a good reading.. on average?

all the final circuits will be 30ma RCD protected however with the DB being metal would i need to install a time delayed RCD before the DB?
 
Last edited by a moderator:
RCBOs within board will be installed

Existing Rod gives a healthy reading 0.30

Ahh mate that cover looks to be the perfect solution thanks, looks quite sturdy i guess you just bury the little stub into the ground?
 
That's an extremely good reading for a rod and would be mad to install a new rod that will probably not achieve any where near that reading.

No need for an upfront time delayed RCD, just make sure the tails are adequately supported and taken through a nylon tail gland .

You could just screw the cover to the floor and conduit down to it or clip down to it and finish it off with a stub of conduit, female adaptor and a stuffing gland.
 
Hello Guys

being a Londoner i have not had a great deal of experience with TT systems in a domestic setting.

The existing installation is in the basement, the existing earth rod is by the DB and sticking out of the ground, not inspection pit is that quite bad?
I was thinking of changing the rod and installing a pit, how long should the rod normally be to make sure i get a good reading.. on average?

all the final circuits will be 30ma RCD protected however with the DB being metal would i need to install a time delayed RCD before the DB?
 
RCBOs within board will be installed

Existing Rod gives a healthy reading 0.30

Ahh mate that cover looks to be the perfect solution thanks, looks quite sturdy i guess you just bury the little stub into the ground?

That is one heck of a low reading for a TT which I assume is in a domestic setting
Was the reading taken with the earth conductor removed from the met ?
 
I would say that if it’s buried in concrete then an earth electrode test wouldn’t be very practical and an earth fault loop impedance tester will be more than adequate
 
That's an extremely good reading for a rod and would be mad to install a new rod that will probably not achieve any where near that reading.

Thank you lee, the sub station is one road away so that's possibly the answer, I agree and it's a very good idea to add some surface inspection port to protect it.

I read up on the RCD on the rails and I agree it would just be a waste of time passing the problem further back.
 
There is no need to install a time delayed upfront RCD if all circuits are to be provided with 30mA RCD protection.
But if fitting a dual RCD board it would be prudent to do so. Your scheme might have something to say about it as the flexible links within the board, feeding the RCDs have no earth fault protection without having the upfront time delayed RCD. This is also mentioned in the OSG.
 
It would be extremely wise to provide fault protection to the flexible tail links within a dual rcd consumer unit as we all know if a live link was to come into contact with the metallic case then in practically every case with a TT system the cut out fuse will not blow and some poor sod will cop 230 v when touching exposed parts
 
There is no need to install a time delayed upfront RCD if all circuits are to be provided with 30mA RCD protection.
I would agree if the tails where installed using a cable gland or an internal clamp to prevent movement of the supply tails and the board was fitted with rcbos only with no tail links.
I would still however install a separate enclosure with a 100mA time delay rcd before the consumer unit.
Bs7671 is the minimum requirement for safety requirements but it doesn’t preclude adding a bit of extra safety if you will.
That would be just my preference anyway
 
The question asked was “however with the DB being metal would i need to install a time delayed RCD before the DB?”
The answer is no.
It may well be prudent, it may well be mentioned in the OSG, it may be some people’s preference, who knows?
What I do know, is that it is not a requirement of BS7671.
 

Reply to AMD 3 DB on a TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
Big argument with a newly qualified electrician with all the necessary qualifications Had to give him a hand later on during the day, nice DB...
Replies
12
Views
3K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
TT system, existing three phase fuse board recently installed by another spark which only has single phase circuits terminated into individual...
Replies
15
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock