Hello everyone!

I have problem with ammeter switch from attachment. Here is connection diagram, and everything looks fine. But, if we look carefully, we will see that ground and L3 are short connected via 3-4 terminals, when we put switch in L1 position. So, my question is, how it's possible, it looks like short-circuit?
 

Attachments

  • Ammeter switch.png
    27.2 KB · Views: 29
Hello everyone!

I have problem with ammeter switch from attachment. Here is connection diagram, and everything looks fine. But, if we look carefully, we will see that ground and L3 are short connected via 3-4 terminals, when we put switch in L1 position. So, my question is, how it's possible, it looks like short-circuit?
Looks correct to me.

When it's
in o each ct is shorted direct to the star point,
In L1, L1 passes through the ammeter, L2, and L3 are shorted direct to the star point,
In L2, L2 passes through the ammeter, L1, and L3 are shorted direct to the star point,
In L3, L3 passes through the ammeter, L1, and L2 are shorted direct to the star point.

Which is what you want.
 
Looks correct to me.

When it's
in o each ct is shorted direct to the star point,
In L1, L1 passes through the ammeter, L2, and L3 are shorted direct to the star point,
In L2, L2 passes through the ammeter, L1, and L3 are shorted direct to the star point,
In L3, L3 passes through the ammeter, L1, and L2 are shorted direct to the star point.

Which is what you want.
Agree
 
The crucial point here being that the secondary of a current transformer should never be left open-circuit, as a high voltage can be developed across it. This is true generally of current sources: short = OK, open = bad, opposite of voltage sources. Each transformer must either be connected to the ammeter or shorted, and the switch cams must be of the make-before-break type so that there is no open-circuit moment as the switch position is changed.
 
The crucial point here being that the secondary of a current transformer should never be left open-circuit, as a high voltage can be developed across it. This is true generally of current sources: short = OK, open = bad, opposite of voltage sources. Each transformer must either be connected to the ammeter or shorted, and the switch cams must be of the make-before-break type so that there is no open-circuit moment as the switch position is changed.
Correct, that's why there are so many poles on the switch, when it looks like you could achieve the same with just 3.

I suppose people could also miss the details in the switch sequence drawing, it clearly shows overlap in the operation.
 

Reply to Ammeter switch connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
604
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
627
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
Hi, I have a 220v House I want to change this switch to smart switch, but I am stumped, I don't have a neutral so I had to return the switch I...
Replies
2
Views
690

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock