Got an EV (Nissan Townstar EV) in my house, has a Zappi EV charger installed (by myself) and notified via ENA form to Scottish Power energy networks
Now at the outset my house is older and they could not identify the cable size and cut out fuse size
During the intial call I was told that SPEN would provide a 100A service and upgrade my supply to a 100A service for free if needed, anything over 100A would require me to pay for the upgrade
A SPEN contractor changed my cable head and verified my lead PILC cable could not be uprated to 100A, they left me with a new cut out and an 80A fuse
I pressed them and asked them to upgrade the cable to a 100A supply and this was the response I got:
Hi Stewart,
Just to reiterate what I mentioned in my previous email
The fuse you currently have (80A) can provide over 100A for decades without degrading. We would only give 100A if your supply was 35mm Al for instance.
So as mentioned, should your demand exceed the 100A supply provided you will need to go through the getting connected process and arrange for a new supply.
I hope that makes sense, feel free to call to discuss your options further. For now I will close this enquiry as we have carried out the modernisation that we can.
Kind Regards,
So, now an 80A supply is deemed a 100A supply when they feel like it.
Now at the outset my house is older and they could not identify the cable size and cut out fuse size
During the intial call I was told that SPEN would provide a 100A service and upgrade my supply to a 100A service for free if needed, anything over 100A would require me to pay for the upgrade
A SPEN contractor changed my cable head and verified my lead PILC cable could not be uprated to 100A, they left me with a new cut out and an 80A fuse
I pressed them and asked them to upgrade the cable to a 100A supply and this was the response I got:
Hi Stewart,
Just to reiterate what I mentioned in my previous email
The fuse you currently have (80A) can provide over 100A for decades without degrading. We would only give 100A if your supply was 35mm Al for instance.
So as mentioned, should your demand exceed the 100A supply provided you will need to go through the getting connected process and arrange for a new supply.
I hope that makes sense, feel free to call to discuss your options further. For now I will close this enquiry as we have carried out the modernisation that we can.
Kind Regards,
So, now an 80A supply is deemed a 100A supply when they feel like it.