Discuss AND gate for S-Plan DHW priority in the Central Heating Systems area at ElectriciansForums.net

Reaction score
0
Does anyone make a 230V AND gate: two mains inputs and which only outputs (2A max, say) when both line inputs are live? I have an S-plan system with two DHW cylinders and need mains output when the heat demand from both ceases (i.e. when both cylinder stats are in the ‘satisfied’ state).
This would be used to tell a weather-compensated boiler that it was OK to drop the flow temperature if the outdoor sensor said so.
 
Does anyone make a 230V AND gate: two mains inputs and which only outputs (2A max, say) when both line inputs are live? I have an S-plan system with two DHW cylinders and need mains output when the heat demand from both ceases (i.e. when both cylinder stats are in the ‘satisfied’ state).
This would be used to tell a weather-compensated boiler that it was OK to drop the flow temperature if the outdoor sensor said so.
Why not just use the satisfied terminal on the cylinder thermostat?
 
Yes - it needs a relay or equivalent because live output is needed when both stats are satisfied and not just one. Otherwise the unsatisfied (still demanding) cylinder could be heated to less than its set-point in the summer when the W/C ramped down the flow temperature sufficient for the CH but not DHW.
 
Hi sounds like an interesting project!

Use each tank stat to pull in a relay.
Then you can link your signal wire thru a NC contact on each relay. (in series)
You can use your NO contacts for the hot water control.
 
Hi sounds like an interesting project!

Use each tank stat to pull in a relay.
Then you can link your signal wire thru a NC contact on each relay. (in series)
You can use your NO contacts for the hot water control.
This is the only way I can see it working.
 
You only need one relay.
Connect the orange of both dhw valves to the coil (I assume there is a valve for each cylinder)
Live to the common, N/O fires the boiler and N/C signals the the weather comp.
 
It sounded like one cylinder would still be receiving input,until the last to be satisfied,signalled it was.
We may need more description of the system set-up.
 
It sounded like one cylinder would still be receiving input,until the last to be satisfied,signalled it was.
We may need more description of the system set-up.

Yes, with two cylinders there is normally two motorised valves.
The OP needs a signal when neither valve is calling for heat,
 
Is it a bit like Power from one source (if present)
is only switched, passed thru ON if single relay is also(AND) energised to pass it ( But things can go wrong is N/C contacts are used for anything )
 

Reply to AND gate for S-Plan DHW priority in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
693
HI Folks. This is my first post so apologies if it's in the wrong location. I recently installed a 3kw Solar system with an iboost diverter...
Replies
15
Views
5K
To start with it all seems to make sense, the TRV measures the room temperature and controls the radiator temperature to suit, as the water flow...
Replies
8
Views
3K
Hello all! I'm a plumber and have a customer where the s plan is working fine for both zones (ground floor, 1st floor + cylinder) but not firing...
Replies
12
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock