Discuss another unfloor heating question in the Electrical Tools and Products area at ElectriciansForums.net

P

Philip657

just about to start a 40sqm underfloor heating job
and want to pick some experienced minds :)
i have worked out that it is going to draw 5600W so 24A
its a 10m run so i have worked out i can use a 4mm cable with a 14v drop and a cable rating of 26a. can i get away with this ? or am i going to use a 6mm ?

looking at the tec spec of the thermostat and its only rated at 13a so i am thinking of using a contactor. my question is is this the best way ? should the contacter be local ? and can anyone recommend a good contactor make ? as i have never had to use them before like this .

is there any hits and tips people have found that may be of use ?


Thanks Phil
 
Im thinking the under floor heating may not function correctley and burn out. max volt drop is 11.5volts, 5%, it may work but it might have a shorter life. up the cable size. better to be safe.
 

Reply to another unfloor heating question in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

I'm after some advice please, I have carbon mat underfloor heating throughout my bungalow, each room has its own thermostat and are fed via a...
Replies
1
Views
793
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
666
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K
In July I moved into my new home with Schluter DITRA heated floors in the bathroom. The floor quit working in December, and my GC and a rep from...
Replies
0
Views
343
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
998

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock