    Any quick calcs to get a rough estimate min Zs allowable for protective devices MCB, BS-88 etc, Im thinking in an exam saves time even looking at the tables if there's a fast ball park check rule of thumb.
     
  2. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    Do you mean max Zs?
     
  3. rich3009
    Offline

    rich3009 Regular EF Member

    Location:
    Lincolnshire
    yes sorry of course
     
  4. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Top Poster Of Month

    Location:
    Northamptonshire
    Takes seconds to look at the Tables.
     
    • Like Like x 2
  5. Leesparkykent
    Offline

    Leesparkykent Super Moderator Staff Member Super Moderator

    Location:
    Kent
    (UoxCmin)/Ia
     
    • Agree Agree x 1
  6. rich3009
    Offline

    rich3009 Regular EF Member

    Location:
    Lincolnshire
    It's a good check though
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    Zs < V/ 5In for B type. e.g.for a 32A . Zs < 230/(5 x32) i.e. 230/160 = 1.4375. ( then apply correction factors).
    Zs < V/10In for C type.
    Zs < V/20In for D type.
     
    • Informative Informative x 2
  8. rich3009
    Offline

    rich3009 Regular EF Member

    Location:
    Lincolnshire
    I knew I'd seen something like this and I remember rule x10 for C and D types, anything for BS88
     
  9. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Top Poster Of Month

    Location:
    Northamptonshire
    Not sure how these quick calculations will save you time if you have the Tables to hand, it is just something else to remember.
     
  10. Zdb
    Offline

    Zdb Regular EF Member

    Location:
    UK
    Quicker just to turn to page 58 in the big yellow book.
     
    • Informative Informative x 1
  11. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    You’ve forgotten cmin so it’s 1.37ohms for 32 amp type B and not 1.44 :)
     
    • Like Like x 1
  12. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    not forgot. stated in post to apply correction factors.

    anyway, cmin is to allow for voltages below 230V. what about when the voltage is > 230V. ????
     
  13. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    Thought you meant the 0.8
    I’ll apologise
    Type D tho is 230x cmin /10In for 5 second disconnection time circuits and 20In for 0.4 second circuits
     
  14. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    agreed. was just considering the 0.4 secs, as most circuits (apart from distribution ccts) are 0.4,
     
  15. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    We have to use the worst case scenario as given in the regulations or use manufacturers data.
    As we know the voltage measured could be anywhere between 230-250 v or whatever really.
    You know what they are like regarding changing regulations and moving the goalposts
     