Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong polarities tripping mcbs before but not this.
The outside front door light live conductor was wired into the lightswitch inside but the neutral was wired into the metallic switch earth terminal - thus using the earth as the neutral. Obviously the light bulb itself was stopping a short circuit which is why it had been used for considerable time without blowing the rewirable fuse I'm just wondering if there is a scenario, other than a break in the earth, where someone could get a shock through this setup? excuse my absent-mindedness as this job has been a nightmare!
Incidentally, the customer admitted wiring the neutral into the cpc for the front door. In his words - "I just did trial and error until the light came on"
I need to start writting note for my memoirs lol
The outside front door light live conductor was wired into the lightswitch inside but the neutral was wired into the metallic switch earth terminal - thus using the earth as the neutral. Obviously the light bulb itself was stopping a short circuit which is why it had been used for considerable time without blowing the rewirable fuse I'm just wondering if there is a scenario, other than a break in the earth, where someone could get a shock through this setup? excuse my absent-mindedness as this job has been a nightmare!
- The bathroom timer fan permenant live was a cpc (from the kitchen downstairs!),
- The kitchen lights neutral was connected to / going through the socket circuit neutral!
- The garage power, spurred from an outside socket [unglanded / failing ip] which itself was a spur off a spur, failed IR tests. The outside socket was also feeding a dozen normal/indoor extention leads on the patio
- The outdoor lights (except the front door one, above) were using CPCs as live conductors and some of them were even cabled in what looks like data cable!
Incidentally, the customer admitted wiring the neutral into the cpc for the front door. In his words - "I just did trial and error until the light came on"
I need to start writting note for my memoirs lol