Doing my assignment for Three phase motors and one of the questions is for Torque. The assignment is due on Wednesday and I had the assignment finished ages ago but other people from my class have only just started it. One of the guys has got most of the same answers as me but then theres a change in the answers when torque is introduced so its making me second guess myself. Can someone give me some advice on it or different torque equation other than the one im using so i can double check it myself. I spent like 5 hours doing this one question because of all the maths involved in it.

A 415 V, 3 phase, 50 Hz, 4 pole star connected induction motor runs at 23 rev/s on full load. The rotor resistance and reactance per phase 0.25 ohms and 3.75 ohms respectively. The effective rotor-stator turns ratio is 0.87:1


a. Using the formula to calculate the synchronous speed:
Ns = f/p
50/2= 25 revs


b. Slip speed is calculated by the formula of:
6ZjLGCK7f7pVq_wyrg2rDquj80exACeE9-g3hRDOejed5qfLib91O8EPJgVWSBQmQMgS1Rv9eOBu7pLuoxaUlnNWBxVi5NTeb7xwzWuqvqsMldWVqidGUyureQ

25-23/25= 8% slip.


c. To work out the full load torque we first must work out the phase voltage:
Phase voltage, E1 =415/√3= 239.6volts
To calculate the torque:

M3gISki6wnpHjf9Bxat2g8g2xxGxVvnU7cuiZtBpBINAa93bgDrl624BZrrVf8tBnkRVQRGsgclfZD6pAPAVbN7B3Y6fhD28xRhA89PysSsB6axcRopUmKNb9g
1xPiFn3jIPalMmtNh1PBeLQF1_UYWBdR5gOaoipnWcUIqn_8b5s9Y3-27NHcKGbywopKdKYiftQ4-__Jz2NF_r2idvYEP3CaY4ubBLNDI97wmIzX2-uzf5YlYw


d. To work out the power output if the mechanical losses amount to 800 W
Use Formula:
qXcibEFR-kB09Wt9Z8uN2RZEJh1Z3zbhwNZW9JW_ZAVUOpT8lVTp_ABCIKczxARCnxh96yPTDGua1QAZkFCVjMDDw53LJ1GnJK61seod9DvFOZzw7EDFzzP8JA


2 π (23)(109.17)= 15777 watts
So Power output - mechanical loss = 15777-800= 14.98KW
e. the speed at which maximum torque occurs:
We first calculate the slip of the torque which you do by the formula:
4mS04yDiVkD872gXE3B-TUjk0CCoqq9ZGEufat5_WiyyQwHn1gFf1OmJ47FVAKImaSFZJ0YkooS7Zz3WNiO-yRp4QVlBx1RfwP-wfy5D3FR9KvMnrOCvqgPFXw

s=0.25/3.75= 0.067
Formula to use to calculate maximum torque:
dE6LUeFO1pBojfsHZVB6Oz7URycwcEK3FtskQneFmhg4jtwqSdlTE1Il2oldvK0ZJ0b344ZptGoktWPBDd7-sHqelXWRe4sVFnndBnudG5SJsTw2iUIWuWX6rA
eXWiUC2Mw7l6BBhkWh4_78vfmPUHy20ejZGA8HpA3FHPXz3zYbFEwNwBCvWUdsDEvyKudchm32zBekMiZL5yD5I-gCT9-CDUMBUFct_SLYcVJainFS3NPx0PCg


Maximum Torque = 111.54Nm



To get the speed when maximum torque occurs we need to use the following formula:
Ce55xBEAkS6-OG_t4vcC65HCdsXZ64PBmQ-qY8BWqSV1jcfjzh2oY6wio9ROib91IsK9Ozl0z_h8S0kSnwlj-VgbZ9ARz_cNwYyMAx81aw1GoxEbOqYvKeYf

0.067= (25-nr/25)
(0.067)(25)= 25-nr
nr= 25-(0.067)(25) nr=23.325 rev/s or 1400 rev/min


f. the starting current use the formula:
kVamnkZGb7n4i34Sb3AZACQJNjNAW5283WmbfbkpUJTASzGiHFZkSuwvICynlCiJkcoOEtKrUiW9T2NLV45P-nRx04CORQOgW3H_tPKK3uO_ndYKQ2DmN7574w


Starting Current is 55.46A
Wow this is huge post now hope someone can follow it and see where ive went wrong



 

Reply to Anyone good with torque equations? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K
J
Hi everyone, On the drawing it says the system's TN-C-S with declared Ze = 0,008 Ω and prospective fault current declared as 50kA When I...
Replies
28
Views
14K
JuniorSparky
J
hi can someone help I have the 301 exam coming up in a few months. I have been trying to some maths samples, the problem is when there is a...
Replies
3
Views
3K
spikester
S
M
Hey guys I've got 301 in two weeks time and I've been given some past papers will post some more soon hopefully. feel free to have ago and post...
Replies
16
Views
5K
Monks
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock