Im adding new circuit to a flat and will need the supply characteristics for the cert. There is a main/main fuse in the meter cupboard upstairs next to meter, but i ryfield i need to mention. Just had a thought possibly the board in pic might not contain fuses as theres one outside hes front door. Its an old block maybe 1950'sit's just a cutout with loads of fuses, normally owned/property of the DNO (but not always) something the average electrician generally shouldn't be touching. Why do you need to know?
Yep thats what I guessed at initially while looking, the holders are very stiff so didnt take it out. Theres BS88 outside hes front door upstirs on the 4th floor, has no markings on the fuse itself but has 100 on the holder. Its not "normal" to have 2 main fuses to a small flat is it ?? Maybe it was back then when they built it !Multi way unit, DNO or BNO owned usually, distributed across 3phase's, the one in picture is 60A me size fuse.
Yep that board is directly above the incomer, its TN-S as you say the armoured strap is visible.From its age I would suggest TN-S and you can see a copper strap from the service head but there is a possibility the neutral is connected to earth within that board. Where does the DNO service cable enter.
Put it down as NV.
Yes theres none on any of them.All the screws are missing on them holders, which are used to seal the cut out fuse.
Always feel like im missing out on something with a NV on a cert. It should not be any higher than 60A but will NV it. Any idea of what fuses would be in there, BS 88's perhaps ?Put it down as NV.
BS1361Always feel like im missing out on something with a NV on a cert. It should not be any higher than 60A but will NV it. Any idea of what fuses would be in there, BS 88's perhaps ?