The load current of the circuit should be unlikely to exceed for long periods the current carrying capacity of the cable (regulation 433.1.204). This can generally be achieved by:
(i).....

(ii) not supplying immersion heaters.....

(iii) connecting cookers, ovens, and hobs with a power exceeding 2kW on their own dedicated circuit.

Now a timer that supplies a 2kW immersion heater, programmed to come on for one hour in the early hours, has been fitted to a FCU that is spurred off a RFC.

Am I being unreasonable in insisting a new circuit is run in for the immersion?
 
Am I being unreasonable in insisting a new circuit is run in for the immersion?

You are a more powerful electrician than me,I can only suggest to people what they should do,if I did insist my clients may tell me with words to the effect of "walk gingerly out of the door"

On a new installation,given the circumstances I would also be concerned about the rest of the installation
A fine tooth Comb may be required
 
Am I being unreasonable in insisting a new circuit is run in for the immersion?

You are a more powerful electrician than me,I can only suggest to people what they should do,if I did insist my clients may tell me with words to the effect of "walk gingerly out of the door"

On a new installation,given the circumstances I would also be concerned about the rest of the installation
A fine tooth Comb may be required

Embarrassingly, this has been picked as a QS review issue, the insistence is for us to put this right.

The rest of the install was not done by us.
 
My own opinion is that an immersion on an RFC is OK if the immersion is only used as a back-up for the main DHW heating system (eg a boiler).

If it is the primary herating source then a separate circuit is needed.

The often misunderstood App 15 is informative and for guidance only. But some QS have their own particular bees in their bonnets, so you may have a hard time.
 

Reply to Appendix 15 (Informative) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
214
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
847
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
In our house the main fuse is rated at 100A maximum. The individual circuits in the consumer unit, if all used simultanuously, add up to much...
Replies
38
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock