Discuss Arrow Switchgear in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
74
image.pngMorning All, Just got this through from a colleague looking at a commercial gas boiler installHe sent this picture through, From the description of the cable coming in it sounds like MICC, but the glands don't look like MICC glands and neither does the cable, So it could just be old flex.
The switc IMO looks like a DP switch but I've never heard of arrow switchgear and cant find any traces on the web, Has anyone heard of them or have any better ideas as to what this could be? As I say It's in the vicinity of a gas boiler, But as of yet my colleague cannot find what it could isoate?
 
Last edited:
Yes as above That is bare MIC cable and MIC glands. If you need to replace the switch there are plenty of alternatives on the market Just find out what load you are pulling though i,t I'm guessing its about a 45amp or 32 amp double pole. Might even be 20 amp Judging by the size of the able
 
Last edited:
All looks pretty bog standard to me too. The switch inside will be a QMB long break type with brass blades that swing into contact forks. Old design, pretty bomb-proof, I think they were DC rated too.
 
Don't know how you blokes are getting all this info from I can't even see the picture
 
Got it now thanks
MICC non covered, no info on the Switch though, sorry
 
Last edited:
IIRC 15A rated, maybe 20. Presumably the boiler only needs a few amps
 
Thanks for the help chaps, Thought It would be a standard DP switch, But with it not being a brand I know about I wasn't sure if it was a more specialised piece of equipment. I didn't think the glands looked like MICC glands, But then again It's been a while since I last had any dealings with it.
 

Reply to Arrow Switchgear in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
452
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
830
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
875
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
882

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock