Discuss Back up generator to mains? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
What is the best way to do a back up generator installation?

I have a guy who wants a 3KW generator (only to power some lights and a pump) but never done one of these installs before, I'm assuming commando socket outside wired to changeover switch??

Thanks
 
first you will have to split the circuits you want backup power to.
i would suggest a small DB for the protected circuits, then as you say a changeover switch and an appliance inlet outside to plug the generator into.

remember the board will need rcd protection and you will need to provide an earth if the main earth is provided by the dno as you cant guarantee that it will be there in the event of a fault.
 
Several recent threads on this topic - have a search - but you absolutely can’t rely on a genset that small having anything remotely like a conventional TNS earth, it will be as floaty as a cloud.
 
So you will have to make the N-E link yourself. Use a transfer switch that is designed for the purpose as it will provide the necessary contact clearance and forcibly prevent the two sources being interconnected. By Commando socket I assume you mean CEE17 inlet (and appliance coupler on the genny umbilical.)
 
can’t rely on a genset that small having anything remotely like a conventional TNS earth, it will be as floaty as a cloud.
Maybe, maybe not ...
So you will have to make the N-E link yourself.
And possibly remove the earth from the centre tap of one of the windings. Not uncommon to find that there is 55V N-E and 165V L-E. Two 110V windings, parallel for 110V, with a winding CT to earth to make 55-0-55, and it ends up at 55-0-165 when the windings are put in series for 220V.

As discussed in other threads (here and elsewhere), you have a fundamental problem if you don't hardwire the genny. If you hardwire it, you can make sure the correct N-E linkage is made so that circuit protection will work(ish).
But if you provide a power inlet, then you have no control over what someone may connect to it. You can't put a N-E link on the fixed side as that would cause a short if one of those 55-0-165 gennys were plugged in - and I would bet that a lot of them don't have double pole protection so wouldn't trip due to this. But you can't not provide it as otherwise there isn't a N-E link if the genny is fully floating.
Personally I think there's an argument for treating it as if it could be an IT supply - as long as all the bonding is in place, all it means is that nothing will trip on a first fault, but without removing covers, that first fault won't actually create a dangerous voltage that can be touched.
first you will have to split the circuits you want backup power to.
I wouldn't bother. The householder will quickly work out that a small genny will collapse if they try using the shower, or the kettle at the same time as other things, and so on. Even if you split circuits, it'll not stop someone moving the (e.g.) kettle to a genny backed circuit. And however you decide to split them, it will always be wrong sooner or later.
Simpler to just do the whole installation and educate the householder in turning stuff off.

And, a 3kW portable genny is likely to struggle to trip most of the OCP devices anyway. It won't trip a B32 on a socket circuit, and it may or may not eventually trip a B6 on a lighting circuit. So most of the protection is going to come down to the built in protection in the genny.
 

Reply to Back up generator to mains? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
Hi All Had an enquiry about installing a generator fed UPS to a house. I have a minimal amount of experience with UPS but am certainly no expert...
Replies
3
Views
1K
My house had previously been wired for a generator (probably not by code to this day) but previous homeowner disconnected and instead hooked up...
Replies
1
Views
528
Just a query. As people have been asking me about changeover switches and generators. If a domestic house already has PV solar, and customer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock