Currently doing a course in Electrical Control Systems. We've gone through a lot of basic electrical theory. One thing we haven't really gone through though is how to select proper size wires/cables.

Was googling this topic and I came across diydata.com
Apparently, a wire with a core size of 1mm^2 can handle current up to 14A from 240V supply. Didn't think this was possible. Thought it would only take a small amount of current. How would you calculate this anyway? Is it Ohm's Law? V=IR so I=V/R (R being the resistance of the copper cable?)

Could anyone give me an example of the first time they had to select cable for a job and being a position like me, were a little unsure and what the results were?

Cheere,

Phil.
 
Hi all,

Currently doing a course in Electrical Control Systems. We've gone through a lot of basic electrical theory. One thing we haven't really gone through though is how to select proper size wires/cables.

Was googling this topic and I came across diydata.com
Apparently, a wire with a core size of 1mm^2 can handle current up to 14A from 240V supply. Didn't think this was possible. Thought it would only take a small amount of current. How would you calculate this anyway? Is it Ohm's Law? V=IR so I=V/R (R being the resistance of the copper cable?)

Could anyone give me an example of the first time they had to select cable for a job and being a position like me, were a little unsure and what the results were?

Cheere,

Phil.

Every job is different, and there are variables to consider, but I’ll come back to that…

The simplest calculation is to divide the power rating (Watts, always given on the appliance) by the supply voltage. That tells you the designed draw of current.

If you want to size a cable correctly, you have to bear in mind the following -

The cable has to be rated at more than what the load will be demanding eg a 9kW shower will draw (9000watts/230volts) = 39 Amps. The cable has to be able to handle that, continuously.

I’d run a 10sq., which is rated at 52 Amps. People with experience of domestic installation might disagree.

And you then size your protective device so that it will protect your installation accordingly. (statement edited out here)

So get a breaker rated between 39 and 52 Amps. Let’s say 40Amps. This will allow the current that the load needs, to pass. And will trip long before the cable is endangered.

But there’s a number of variables to consider -

a)the ambient temperature that the cables will be working in (surrounding cables in insulation means they'll be hotter than if they were clipped to a wall. This heat has obvious danger implications = ’ bad thing’ and also leads to greater resistance to the flow of current. = ‘another bad thing’)
b) the grouping factor. Cables bunched together don't cool down so efficiently.
c) the volt drop. The longer the length of run, the more the voltage drops. There’s a rule for that too.

A couple of examples and a quick formula -

Iz = In/(Ct * Cg)

Iz = continuous current-carrying capacity of the conductor - in other words, the size needed
In= Protective Device rating
Ct= Temperature correction factor
Cg= Grouping Correction factor

Ex 1
A copper cable supplying a heater that is taking 23 Amps (Watts/Volts) in an ambient temperature of 30C. It’s on it’s own, on cable tray.

Iz = 25 / (1*1)

The breaker is rated above the load being drawn, ie 25>23.

Above gives you 25 Amps carrying capacity needed. The book says that in these conditions, 2.5sq will take 30 Amps.

The (1*1) just means you don’t have to make any allowances for temperature in this job - the book quotes for conductor ratings are based on a baseline ambient of 30degreesC, and that’s what we have. And it’s on it’s own, so no correction needed.

Ex 2
Same scenario as above, but now the ambient temperature is 50degreesC

Here we have to adjust the temp. correction factor, because we’re running hotter. The obvious effect will be to increase the size of cable required. It’s still on it’s own, so don’t change the grouping factor which stays at 1.

Iz = 25 / (0.71*1) the book says if you have 50degreesC, you have to apply a correction factor of 0.71
Iz = 35.2 Amps.

You have to upgrade to a 4sq. Now, which can take 40 Amps. Because you’re in a hotter environment, 2.5sq won’t do. The job just got more expensive.

Ex 3
If you had that job to do, in 50degreesC, running on tray with say, 4 other cables you’d have to factor that in too…

Iz = 25 / (0.71*0.8) (You get the 0.8 from the regulation tables. Different situations will give you different numbers to plug in)
Iz = 44 Amps.

Now you’re up to using 6sq. which takes 51 amps. Your 4sq just got too small for the job.
 
The other thing to consider is Volt Drop.

You multiply...

the milliVolt drop/amp/meter for a particular cable - from the book
x
the design current of the circuit - (Watts/Volts) or Ib
x
Distance of the run, in meters

… and just hope that your answer (in Volts) is less than 4% of supply voltage. So for a domestic supply, the volt drop can’t be more than 9.2 volts. Otherwise you have to size up again.
 
That’s all… theory. Lads doing this stuff all the time use experience and judgement. I don’t do domestic installation so I’m just giving you the theory.
Hope that helps.
 
Last edited by a moderator:
This is a new one on me, if this is the case why does it trip when the appliance develops a fault

You're quite right, and thanks for pointing it out.

Looking at my old notes I see that ''the priority of the fuse is to protect the circuit conducors, not the appliance.''

But fuses ain't breakers, and I overstated the thing anyway.

Apologies to all, and thanks again - my o.p. edited now.
 
VD is now 5% of supply voltage, for 230V = 11.5V.;)

But not in Dublin, seemingly ;)

I think the latest (4th) edition of the ETCI rules came into force at the end of last September, and it seems from this Cable Calculations that the max. is still 4%. Couldn't vouch for that site/quote, as I don't have a copy of the 4th.

Interesting, as I imagine we'd tend to follow UK best practice. And sure, why not ? :D

Did your rules change to 5% just with the 17th edition, and when did that become current ?

I've not come across the 3% for lighting before. What would the thinking be behind that ?
 
I see.:)

The 17th ed came in on 1st July 2008. This is also when the new VD tolerances came in.

I would say the lighting VD tolerance was lowered to try and improve efficiency thereby reducing wasted energy in a circuit,as we know lower volts = higher amps.
 

Reply to Basic Question on Selecting Cable in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
348
Hi Everyone, Sorry for all the questions. With he help of a friend, I recently installed some insulation into my mother's loft. Whilst adding...
Replies
3
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
203
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
908

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock