Search the forum,

Discuss Bathroom Downlights 17th again? in the Australia area at ElectriciansForums.net

B

bathroomboy

At the customers house today to decomision shower circuit in prep for bathroom refit (mixer shower replacing) tns supply, old wylex cu with plug in mcbs, question is do I really need to protect new bathroom downlights with an rcd, no cables will be sunk in the wall and further more downlights are out of the zones at 2.25 mtrs.
Thanks again
 
Hay mate.

I'm afraid that all circuits within a bathroom must be 30mA RCD/RCBO protected regardless of any other factors.

Cheers.
 
Thats what I was thinking got my 6382 booked for April, anyway back to the job in hand as stated above, tns supply,6 way Wylex cu with plug in mcbs, dodgy looking earth from met to cu solid green looks to be about 4m/m, can replace this, equipontial bonding to gas and water in 10m/m.

Options: lighting circuits are seperate, I don't suppose any one makes a plug in rcbo, could put in a stand alone rcd on the upstairs lighting circuit but would I possibly have any problems with borrowed neutral on landing two way switch.

Old decommisioned shower circuit 6m/m could be utilsed to feed bathroom lights, at present stand alone seperate breaker from wylex cu, could be replaced with stand alone rcd.

Put local fcu rcd in airing cupboard inside bathroom which also houses combi boiler which has no supplementary bonding.

Thanks again
 
As been said ALL circuits in bathroom need 30mA RCD protection, especially the shower.

You could use the existing 6mm for lighting and fuse it down in a sep CU along with the new circuit for the shower.
 
There will be no new shower circuit, new shower mixer running off combi boiler hot water feed, so 6m/m cable avaiable from cu to attic, I'll probably change stand alone breaker to an rcd cu unit with with 6 amp mcb for bathroom lights. Thanks again.
 

Reply to Bathroom Downlights 17th again? in the Australia area at ElectriciansForums.net

Similar Threads

I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Looking at a bathroom modification and wouldn't mind some input on the need for RCD protection. Bathroom has existing light and wall fan...
Replies
41
Views
10K
Hi Guys & Girls, It's been a while, hope everything is good. I have an issue that's proving to be a bit of a head scratcher. Please bear with...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top