Discuss Bathroom junction box lighting in the The Welcome Forum area at ElectriciansForums.net

Shaq

-
Reaction score
0
Hi, im trying to fit spot lights in a bathroom.. the main is currently out of a wall with a small amount of cable on it, can I use block connector with black tape and sink it so I can extend the wire to run further from the bath? If not can I use an ip65 rated jb sitting about 170mm away from the bath and 2.25m high from the floor?
 
can I use block connector with black tape and sink it so I can extend the wire to run further from the bath?
NO! you cannot make a connection like that and hide it in the wall.
I guess you have access to the loft above?
Go there and find the cable. Make the joint up there.

PS when you say
the main is currently out of a wall
What do you mean? is this a permanent live, or is it the switched live and neutral from a previous light fitting?
 
This is the main permenant live and its only about 4inches worth of wire to play with. Was told I can use a waterproof junction box?
NO! you cannot make a connection like that and hide it in the wall.
I guess you have access to the loft above?
Go there and find the cable. Make the joint up there.

PS when you say

What do you mean? is this a permanent live, or is it the switched live and neutral from a previous light fitting?
 
Hi, im trying to fit spot lights in a bathroom.. the main is currently out of a wall with a small amount of cable on it, can I use block connector with black tape and sink it so I can extend the wire to run further from the bath? If not can I use an ip65 rated jb sitting about 170mm away from the bath and 2.25m high from the floor?
any RCD PROTCECTION on that circuit ?
 
Hi, im trying to fit spot lights in a bathroom.. the main is currently out of a wall with a small amount of cable on it, can I use block connector with black tape and sink it so I can extend the wire to run further from the bath? If not can I use an ip65 rated jb sitting about 170mm away from the bath and 2.25m high from the floor?
Only if you are registered with one of the C,P,Schemes
 

Reply to Bathroom junction box lighting in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
981
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi, Hopefully I haven't made an error but I was speaking with another electrician and he said standard junction boxes with screw terminals can no...
Replies
3
Views
855
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock