Discuss Bedroom socket extension in the UK Electrical Forum area at ElectriciansForums.net

ConH85

DIY
Reaction score
0
I’m after some advice. I have a single socket in a bedroom where I’m putting some panelling. On the panelling I’m wanting 2 double usb sockets (one each side of the bed).

First question: Should I install a 20A unswitched flex outlet plate in place of the single socket to feed the 2 double usb sockets with some 2.5mm flex behind the panelling?

Second question: Would I be able to add a fused spur from each double socket to feed a wall hung lamp either side of the bed?
 
The answers depend on whether this existing socket is part of a ring final circuit (32A circuit breaker) or not.
simple enough to extend the ring to both new sockets.

Even if its a radial circuit (16A) supply. Can branch off to wherever you need it.

and dont use flex. Use the proper 2.5mm twin and earth solid cable.
 
first thoughts is if you no longer need the single socket, replace with a 13A Fused connection Unit. then spur off to your 2 new sockets. then a 5A FCU from each new socket for each lamp. ( or just 1 5a FCU from 1 socket to feed bothe lights).
 
It’s a 32A ring main. Sorry, forgot to put that. I would put a 13A FCU in place of the single socket but if the fuse was to go it would be behind the panelling.
 
It’s a 32A ring main. Sorry, forgot to put that. I would put a 13A FCU in place of the single socket but if the fuse was to go it would be behind the panelling.

Either way you need access to the socket or FCU. Just in case there is a fault in future and someone has to get to the area.
Don't hide it behind a panel.
 
IF the existing socket has two cables coming into it, and these are confirmed by testing to be the two legs of a RFC, you could join a short length of 2.5mm2 T&E to them, using maintenance free joints only, you could then close in the front of the existing box with a blank plate, and feed the new cable to a fused connection unit mounted on the new panelling. This doesn't necessarily mean that it has to be mounted directly in front of the old socket, but it should be positioned so as the buried existing cables are still in safe zones, as defined in the regs. Mounting it in front of the old socket will ensure this, but there may be other places it can go as well.
You can wire your new sockets and lights from this fused connection unit, using appropriate sized T&E, once again ensuring it is fitted in the safe zones, if concealed.
As you can see, there's much more to this than you might think at first sight.
 
IF the existing socket has two cables coming into it, and these are confirmed by testing to be the two legs of a RFC, you could join a short length of 2.5mm2 T&E to them, using maintenance free joints only, you could then close in the front of the existing box with a blank plate, and feed the new cable to a fused connection unit mounted on the new panelling. This doesn't necessarily mean that it has to be mounted directly in front of the old socket, but it should be positioned so as the buried existing cables are still in safe zones, as defined in the regs. Mounting it in front of the old socket will ensure this, but there may be other places it can go as well.
You can wire your new sockets and lights from this fused connection unit, using appropriate sized T&E, once again ensuring it is fitted in the safe zones, if concealed.
As you can see, there's much more to this than you might think at first sight.
Great idea. I do have a copy of the regs so I’ll have a look tomorrow. Thanks!
 

Reply to Bedroom socket extension in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
666
Hi there, I am looking for some advice re: putting new sockets and usb sockets in my home. Someone will be rewiring the entire house but I have...
Replies
19
Views
1K
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
876
Hi, I'm a hobbyist without formal training. I'm looking to power audio/video equipment over several hundred feet of extension cords. I have 2...
Replies
4
Views
392
Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB...
Replies
2
Views
727

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock