Discuss Best way of fixing boxes to crumbly walls..... in the UK Electrical Forum area at ElectriciansForums.net

LewisM

-
Esteemed
Reaction score
706
Hi I'm doing a rewire of an old victorian terraced house built in the 1890s the plaster and bricks are extremely fragile even with a hammer and scutch chisel the brick just crumbles away leaving no solid fixing, what is the best way of fixing boxes back square? I've thought about expanding foam but will that not expand and push the boxes back out?

It's hard to see from the picture but the brick is all jageded and in pieces.

PXL_20221101_152913611.jpg
 
A technique I've used in the past is to take a 12" - 18" length of batten, drill a couple of 4mm holes in it at the same spacing as the holes in a fitting, then use 3.5mm screws to attach the batten to the front of the box.
Offer this up to the wall, and nail, wedge, prop or any way else you can think of the batten flat against the wall. Mix up some mortar and pack around the box.
 
Expanding foam will grip very well, but make sure to use a low expansion variety.

CT-1 or similar might also be a good option.

Think I prefer the idea of bonding after priming with dilute PVA.
 
recently Done a few new sockets in a really old crumbly house and I used coving adhesive as an emergency from wickes and that stuff sticks boxes in beautiful and it was cheap as well
I'll give it a go, so just splat a load in the back then push the box in the it holds it firmly while it dries?
 
I'll give it a go, so just splat a load in the back then push the box in the it holds it firmly while it dries?
That is how I did it , make sure you scrap off any excess when its still wet as the stuff dries rock hard
 
Good box in with some adhesive begged off the dot and dab monkeys.
 
As all the above ^^^^

In the past I have used a couple blobs of grip fix to stick all the boxes in position then filled round them after with either bonding or drywall adhesive. This way you can get all the cables in then do the back filling all in one go.

Be sure to prime the brick first ideally with a very watered down pva mix.
 
Hi I'm doing a rewire of an old victorian terraced house built in the 1890s the plaster and bricks are extremely fragile even with a hammer and scutch chisel the brick just crumbles away leaving no solid fixing, what is the best way of fixing boxes back square? I've thought about expanding foam but will that not expand and push the boxes back out?

It's hard to see from the picture but the brick is all jageded and in pieces.

View attachment 103260
What about surface mounting all boxes and sleeve it up the wall or across the wall using PVC conduit
 
Spray it with water and slap some bonding in there.

If you want it to go off quick mix a bit of cement in with the bonding and it'll go off in no time.
Another vote for that solution. Bonding with a bit of cement in the mix.

Do make sure the box is set level. The mix goes off extra quick and hard, so there’s no adjustment later!

Either drill through the box and screw to fix - after the bonding has set!
Or pop out a couple of the knock outs. The bonding will come through a bit into the box and hold the box firm.
 
I hate it when removing a plug the back box comes with it, this resin will fix anything: Rawlplug R-KEM II Styrene-Free Polyester Resin 300ml. if you have not used it before be aware that the nozzles are one use only unless you are quick and have a few to do. 😜

Have mixed it on a board before now when all my nozzles have gone solid, just squeezed out of the tube onto the board and mixed with a disposable stick, not your favourite screwdriver.
 
Last edited:
Another vote for that solution. Bonding with a bit of cement in the mix.

Do make sure the box is set level. The mix goes off extra quick and hard, so there’s no adjustment later!

Either drill through the box and screw to fix - after the bonding has set!
Or pop out a couple of the knock outs. The bonding will come through a bit into the box and hold the box firm.
Bend out the nock outs this creates a much better hold . But again , bonding on a ground floor might not be a good idea . It draws in any damp
 
If you get 1 or 2 fixings drilled first,mix some decent quality drywall adhesive up (use puddle water or bird bath😉,it goes off faster) load out recess,leaving screw plugs visible,push in flush & level,fit screws loose,tighten an hour later.

I have such a property,built 1911,and this method has worked well on the other many dozen i've applied love to.

A very good pal of mine,had a similar issue....and also has a touch of Aspergers.....on giving him the same advice,he listened,and said "....but a period property like this,traditionally had only a yard at the rear...so would not have the option of an ornamental bird bath...." 😀 just can't argue with that...
 
Always used to have a bag of bonding on the van back in the domestic days
 

Reply to Best way of fixing boxes to crumbly walls..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm installing smart modules in my light switches which means I need to replace the existing 25mm back boxes with 47mm ones. Downstairs all walls...
Replies
0
Views
344
Hi Guys, I've completed rewires with hollow walls before and was able to use a dry line Box. No chance of being able to use them this time. I've...
Replies
30
Views
5K
Customer wants 1 single socket outlet turned into double point on his kitchen wall which is tiled already with single box hole cut out Is it...
Replies
14
Views
4K
My first post and thank you for reading. I live in a commercial building that was converted to residential. I have a walk in closet where the...
Replies
0
Views
2K
I posted last week regarding a lighting cable being too short in the wall to reach my new light fittings.this is still annoying me lol, I will try...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock