Hello,

I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may be positioned before or after a RCD but I have always been of the idea that the SPD needs to go before the RCD due to the RCD potentially tripping from a surge leaving the SPD unable to operate correctly.

Can someone please help clear up my confusion on this?



SPD.png
 
Not sure why they have number 7, when number 1 states to connect to a 32A MCB.

I wouldn't connect downstream of an rcd, for the exact reason you mentioned.
Although, i guess there are some situations, where there is a 100mA or time delayed rcd some distance before any consumer unit where the SPD might be fitted....
 
Regulation 534.4.7 covers this, basically the RCD has to have an immunity to surges of at least 3kA and usually that is a selective type (traditionally used as incomers for TT systems, followed by 30mA per circuit (group) for additional protection).

It also advises against fitting a Type 1 SPD after any RCD, and that it might still result in the RCD tripping on a big >3kA surge (with the related issue of loss of healthy circuits).

TL;DR don't do that for RCBO or dual RCD boards.
 

Reply to BG SPD after RCD acceptable? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
898
So I am a fully qualified spark with my own company, however I also have a few properties I rent out. One of my tenants asked if they can have an...
Replies
84
Views
11K
Hello, I have a Clipsal consumer unit with two "ways" unused and blanked off and potentially a third available as the Proteus Geyer B16 MCB is...
Replies
16
Views
4K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock