Discuss Bit rusty on this... after some help please :-) in the UK Electrical Forum area at ElectriciansForums.net

sythai

-
Arms
Reaction score
356
Hi All

Just trying to put together a household/diversity calculation for a new supply to a 2 bed/ 2 bath 'fully electric' barn conversion.

Figures are working out way too high! done as per OSG.

Here's the final set up:

32a ring 1
32a ring 2
4a lighting
40a wall heaters (infrared panels)
26a water heater (Electric boiler)
13a oven
13a hob

After diversity

32a ring 1
13a ring 2
3a lighting
40a wall heaters
26a water heater
11a hob
11a oven

136 amps!!!! (don't think so):openmouth:

What am I missing, if anyone could give me any assistance would be really grateful ?

Thanks Sy
 
"what am I missing"

The OSG "guidance" on diversity dates from a time when properties had 4 or 5 circuits .....

What happens if you add up all the breakers and multiply by 0.25?
 
Thats better 45amps :)

Where does that calculation come from then? Thanks Sy

My "creation" and I think is more sensible with bigger CU's .....

Never been questioned about it on my assessments:)

The reality is that a ring would never pull 32A unless its doing space heating.... a lighting circuit won't pull 3A ........

How big is the main fuse?
 
My "creation" and I think is more sensible with bigger CU's .....

Never been questioned about it on my assessments:)

The reality is that a ring would never pull 32A unless its doing space heating.... a lighting circuit won't pull 3A ........

How big is the main fuse?

I see... know what you mean, does seems more realistic. There is no main fuse as of yet, I'm doing the calculation for new supply coming in
 
Hi - I agree the ring won't have much on it compared with cooking, hot water and heating - for what it's worth, my choice would be 100A service.
 
There is an accepted calculation of 0.4 of total breaker values.
I've never heard of the 0.25 rule, but in some installations I feel it would be more than acceptable.

However it's up to the individual spark to make there own judgement call for an individual Property.

Edit: posted before I'd read "your own creation" Murdock.
 
Why they even opting for infrared heating? Madness imo. Infrared won't necessarily heat the room, it will heat objects, so when it's on it will be just floging away. They may as well dig a hole in the ground and chuck ÂŁ20 notes into it and Set it on fire. I've installed a few of these with wet systems Heatrae Sadia Electromax Electric Flow Boilers | Electric Boilers - https://www.plumbnation.co.uk/site/heatrae-sadia-electromax-electric-flow-boilers/?gclid=CjwKCAjwgr3ZBRAAEiwAGVssneSUIxF-rzASmrW42sEDmOt95x73_qa5hrlRQGjdKSqJ3gbJ2CN-7RoCAAwQAvD_BwE
 
"what am I missing"

The OSG "guidance" on diversity dates from a time when properties had 4 or 5 circuits .....

What happens if you add up all the breakers and multiply by 0.25?
That's similar to what I use...but not with Electric Heating and Electric Boiler.
 
I'm not party to the actual power rating of whatever heaters and water heater will be fitted, but surely you would have to assume no diversity is applied to the actual ratings for these as it's almost certain that all the heaters and the water heater will be on at the same time?
I agree you could reasonably assume some diversity for the other circuits.
 
Looking at a basic all electric house without storage heating it might be considered on average over a range of houses to consume about 30A as a maximum demand value, this is the sort of level that would be applied for a network design.
So you are generally looking to see if you are near this level.
32a ring 1 any ring is likely to only take a 13A load on a kettle for short time and most other applications (some cooking equipment excluded) will be much less than this, any other loading will be exceptional in most houses.
32a ring 2 as ring 1 but if upstairs then a lower loading is much more likely.
So rings at about 20A demand
4a lighting, all LED lighting might draw about 1A and can be pretty much ignored.
40a wall heaters (infrared panels), these will consume a lot of power but in bursts the primary long time period is when first switched on, but 9kW of heating is a lot for a modern insulated house so they would likely not be all on at once and with thermostatic control say half the power demand on average.
So heating at 20A
26a water heater (Electric boiler) this would hopefully be on most of the time so operating occasionally but you would need to account for an initial switch on so not a lot of diversity here.
Boiler 20A
13a oven and 13a hob these two together would use a similar load profile to a 6kW cooker so about 15A
Total load on average about 75A, but overcooked to allow for the boiler at times. This is over the 30A network design but would indicate an 80A supply could be suitable.
I would normally not consider a 60A supply suitable for an electric house (a flat, maybe).
This is just how I might approach things on a practical level.
 
Thanks Richard.... extremely helpful and appreciated, looking more realistic now than the osg method.

Hob and oven fully electric and both come with 13 amp plug tops on already.

Infrared heaters were Clients spec, bonkers I know but they've got some strange ideas and didn't want any alternative suggestions ! Believe me I tried.

Cheers Sy
 

Reply to Bit rusty on this... after some help please :-) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi Guys Got few of these coming up now... 1st fixes done. Now the fun bit of 2nd fixes - bit of a head scratcher as none seem the same! 🤯 What...
Replies
9
Views
1K
Just had three split Air Con units installed at my home, the ones with an indoor and outdoor unit. I (perhaps naively) trusted the installers...
Replies
2
Views
1K
Hi all, I have a regular client who has asked for a battery back up system to be installed at their home. They live in a rural location on a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock