Discuss Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

P

Piratepete

Hi Guys
Doing an EICR of a property.
The client has an outbuilding with gas and water supplies. It has it's own CU fed from the main CU in the house.
The water is bonded but the gas is not.
The water supply is underground from the house in plastic and then changes to copper which is bonded.

The gas supply comes from the house in an underground copper pipe linked to the gas pipes in the house. So, electrically, it would be subject to the bonding in the house.
But does this negate the need to bond it in the outbuilding?

Looking forward to wise words!

Cheers
Pete:confused:
 
Last edited by a moderator:
NO, it doesn't negate main bonding to the outbuildings CU (EMT) especially if the supply is PME, in which case the sub-main earth should be a minimum of 10mm....
 
NO, it doesn't negate main bonding to the outbuildings CU (EMT) especially if the supply is PME, in which case the sub-main earth should be a minimum of 10mm....

I read it that he is saying the gas is bonded in the house and is in copper pipe to outbuilding so is bonded already. The Water they have bonded in outbuilding because it has plastic pipework across to it.
 
I read it that he is saying the gas is bonded in the house and is in copper pipe to outbuilding so is bonded already. The Water they have bonded in outbuilding because it has plastic pipework across to it.

It doesn't matter a jot whether the gas pipe is bonded at the main house or not, it still needs bonding at the outbuilding....
 
I read it that he is saying the gas is bonded in the house and is in copper pipe to outbuilding so is bonded already. The Water they have bonded in outbuilding because it has plastic pipework across to it.

Yes. your interpretation is correct.
My immediate thought was that it should be bonded, but I couldn't understand why it hadn't been done as the gas supply is an easy connection within 2 metres of the CU and all services were put in at the same time, 10 years ago. The water stopcock and bonding point are miles away.
Pete
 
New posts

Reply to Bonding Gas Supply in an Outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
729
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock