Discuss Bonding metallic back boxes. Best practice? in the UK Electrical Forum area at ElectriciansForums.net

Mark42

-
Esteemed
Patron
Reaction score
322
Something about the way this box is bonded feels wrong. I prefer the box to remain bonded even with the accessory removed. Is this method compliant? What do others think? (Ignore missing grommet)
(Taylor Wimpey new build)
778C16DB-397F-4C32-9796-933CF268C045.jpeg
 
The earthing looks ok. In fact as one of the lugs is fixed the bond between the socket and the box is not required, but good practice. As no one should be in there with the power on the box does not need to be earthed with the socket removed.
 
Something about the way this box is bonded feels wrong. I prefer the box to remain bonded even with the accessory removed. Is this method compliant? What do others think? (Ignore missing grommet)
(Taylor Wimpey new build)View attachment 53213
Nothing wrong there Mate apart, from the muck in the box it's a common earth bar. Oh and as Tel says it's not bonded it's earthed
 
and Stevie Wonder did the plastering and decorating?
 
Standard practice

I to don't like the earth twisted around the live but that's just me
Tgat probably happened wholst the socket was being pushed back into the back box, wouldn't have been evident until some one released the socket from the box, youre a hard Man to please DD, lol :):rolleyes::rolleyes:
 
If it's an RFC, it's a pity they didn't take advantage of the dual earth terminals on the socket for the two legs of the ring
 
I think Mark is aiming at a point of very specific detail here. In the UK we have socket outlets with either one or two earth terminals. Historically, for 50 years the convention with a ring final circuit was to connect both legs of the ring to one terminal. Then, a regulation came in that required a high integrity CPC if the expected total leakage on the circuit exceeds 10mA. One advantage of the RFC (and many of our sockets are on RFC's) is that it provides two parallel CPCs which serve the purpose of a high-integrity CPC if they are separately terminated using a dual terminal socket.

In Mark's pic, the socket has dual terminals, not needed specifically as a domestic RFC is not considered a high leakage circuit. But instead of putting the two legs separately in the two terminals, they have put them both in one and used the other for the back box strap. I would say it's fine, but it's a pity not to gain the advantage of the high integrity CPC where dual terminal sockets are installed.
 
Last edited:

Reply to Bonding metallic back boxes. Best practice? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
963
An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K
Hi, New to the forum. I have two very specific questions, for the setup below. Setup details: Currently I have a setup with an outlet used for...
Replies
6
Views
653
Hey, question for the group on grounding when using MC cable and metal boxes.... Situation: Enclosed a carport and turned it into a garage. I'm...
Replies
1
Views
916

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock