Discuss bonding of pipework with flexible connectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

maffa ent

afternoon all!

doing a pir / ecr, whatever you wanna call it now, bonding readings ok on pipework coming from under floor, but not on sinktop or taps, only slightly higher but high enough to be above satisfactory.

what would you do, or recommend, or note?

thanks
 
The earth safety connection should be connected to the solid part of the pipework.
If flexible pipes are introducing a difference in potential, then you should really bridge across to either side of the flexible pipe.
Two earth safety connections one either side of the flexible pipe linked by a conductor.
 
Last edited by a moderator:
If this is in a kitchen, I don't think that there's any requirement.

On Site Guide, Amd 1, section 4.7:
If the installation meets the requirements of BS 7671:2008(2011) for earthing and bonding, there is no specific requirement for supplementary equipotential bonding of:
- kitchen pipes, sinks or draining boards
- etc, etc
 
thanks for the replies.

ok, so if i remember rightly, the requirements for no supp bonding required are:

1 - all rcd protected

2 - main bonding in place

3 - all disconnection times met

all of the above are present, it's just these slightly higher readings from the last, accessible, bits of pipework above the flexi connectors.

the readings are fractionally too high to comply - am i being picky?

don't really want to fit clamps either side of the flexi's, but..................
 
thanks for the replies.

ok, so if i remember rightly, the requirements for no supp bonding required are:

1 - all rcd protected

2 - main bonding in place

3 - all disconnection times met

all of the above are present, it's just these slightly higher readings from the last, accessible, bits of pipework above the flexi connectors.

the readings are fractionally too high to comply - am i being picky?

don't really want to fit clamps either side of the flexi's, but..................

1. There is no requirement for supplementary bonding in a kitchen.
2. Pipes which are deemed to be extraneous conductive parts in a special location only need to be supplementary bonded at the point of entry to the special location....continuity beyond that point is irrelevant.
3. TBH if you are carrying out PIR's/ECR's you should understand the requirements for supplementary bonding.
 
me and my lack of info!

2 instances on this job - kitchen and bathroom.

ok, i understand all that's been said - except for the bit about supp. bonding at entry to the room - haven't heard that before. any reference to where that comes from please?

the requirement for main bonding being in place, in order to be able to omit supp. bonding - i thought all continuity readings had to be less than 0.05 ohms, rather than just saying "main bonding's there, forget supplementary".

with this job, the readings on these small sections of extraneous metal are 0.1 -0.2 ohms (as mentioned the rise is definitely across the braided connectors).

should i bother?
 
Surely it depends what edition the kitchen was installed to?

As in not the 17th?

I know thats the ONE now before someone jumps on me but supp bonding might definately be required in its current state. Don't know can't see it/wander lead isnt long enough :yawn:
 
Surely it depends what edition the kitchen was installed to?

As in not the 17th?

I know thats the ONE now before someone jumps on me but supp bonding might definately be required in its current state. Don't know can't see it/wander lead isnt long enough :yawn:

It's never been required in kitchens....It's always been a myth which I believe came about following an illustration in a guide to the wiring regulations,which showed for reasons unknown bonding between a sink and a socket.
 
me and my lack of info!

2 instances on this job - kitchen and bathroom.

ok, i understand all that's been said - except for the bit about supp. bonding at entry to the room - haven't heard that before. any reference to where that comes from please?

the requirement for main bonding being in place, in order to be able to omit supp. bonding - i thought all continuity readings had to be less than 0.05 ohms, rather than just saying "main bonding's there, forget supplementary".

with this job, the readings on these small sections of extraneous metal are 0.1 -0.2 ohms (as mentioned the rise is definitely across the braided connectors).

should i bother?

The purpose of supplementary bonding in special locations is to prevent a PD between extraneous conductive parts and conductive parts within the location under fault conditions until the protective device clears the fault.
As an extraneous conductive part,by definition, is introducing an earth potential from outside the location,it follows then that by bonding at the point of entry to the location the hazard has been dealt with. It is also permitted to use an electrically continuous ECP as a supp bonding conductor,which is why it is often possible to supp bond outside the location in a more convenient place such as an airing cupboard....but once again,what happens to the pipework within the location is irrelevant,it is no longer extraneous.
 
It's never been required in kitchens....It's always been a myth which I believe came about following an illustration in a guide to the wiring regulations,which showed for reasons unknown bonding between a sink and a socket.


....
Hello WP, yeah I know... I won't go on about it I just meant that irrespective of where it is or was 'required' the general rule still applies be it a study/lounge /kitchen/bedroom.

B
ut yes I know the kitchen is not a special locn
 
why are you doing a pir on the installation ? ie what is the purpose, and is the electrical installation paperwork available from when the db was upgraded ?

If the installation has been brought to 17th standards then surely there is no requirement for supp. bonding anyway
 
pir is simply to assess safety for the homeowner. no certs issued when unit fitted, but we're used to that now eh!

my only concern is regarding continuity to these section s of pipework above the connectors. readings apparently, so my sparky tells me, were 6ohms on the pipework in places. would it just cover all eventualities to bond across the connectors?
 

Reply to bonding of pipework with flexible connectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
866
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hello there all, I'm a fairly newly qualified electrician and have been doing more and more EICRs lately, if someone could actually trawl through...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock