Discuss bonding of water on shower install in the Australia area at ElectriciansForums.net

J

john1980..h

hi all,

need to install supply for shower pump which is hot and cold fed. only a 16a supply required but no rcd on CU. so planning to use rcd spur outside CU to protect circuit.
whilst checking for water and gas bonds, gas is present but although 10mm GY leaves CU cant see it on water pipe because new kitchen has been installed so may be behind units. can bonding be confirmed with a test or do you need to see it.

any help appreciated

john
 
is the water stop tap accessible? if so needs cut a hole above in the unit. the connection should be visible and accessible. if the kitchen is newish, get em back to it as they should not have concealed the earth connection.
 
gs 3 states if a clamp is built in unvisible you can proove continuity using an r2 measurement of less than 0.05page 35

That's not how I interpret it, the words used are "a bonding connection between 2 conductive parts" and "metallic pipes between which a bonding connection was required"

That's not the same as a main protective bonding conductor is it?
 
no work completed by me as yet, just got a feeling new kitchen went in and if pipe work was altered then bonding was probably not reconnected, but was going to disconnect 10mm from CU and test from there to stop tap with wander lead. was hoping for less than 0.05 but is that ok if i cant prove clamp is there and within 600mm?
 
My old boss got inspected by the NICEIC and kitchen fitters had concealed the M.E.B to the water. They insisted that he got the kitchen fitters back to make the termination point accessible.
 
My old boss got inspected by the NICEIC and kitchen fitters had concealed the M.E.B to the water. They insisted that he got the kitchen fitters back to make the termination point accessible.
first bit of common sense i;ve heard from the nic.
 

Reply to bonding of water on shower install in the Australia area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
775
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
638
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
449
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock