Discuss Bonding Size for Old Incoming Supply in the UK Electrical Forum area at ElectriciansForums.net

IAmSparkytus!

-
Esteemed
Arms
Reaction score
315
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted.

No idea what size the incoming fuses are or incoming conductor sizes. Would have to contact the DNO but not sure whether they would give that info to anyone or how long it would take for that matter?

The 200A fuses feed a busbar chamber which we are tapping off with 70mm tails and 35mm earth to feed our DB.

Can our bonding be sized from that - 25mm?

Would 16mm suffice?
 
What is the earthing system and what is the size of the earthing conductor?
Can’t really tell as the cable goes straight into the cabinet. Doesn’t look to be TT as there are no overhead lines in the area.

What relevance would knowing the incoming fuse size make.
Just trying to give as much info as I know as possible, apologies if that troubled you 😬
 
Can’t really tell as the cable goes straight into the cabinet.
Can you really not see it anywhere?
Nothing to lose by asking DNO what their records say.
Seeing if PEFC and PSCC (phase to N) are similar or wildly different might give you a further clue.

As you probably gathered you need to know whether you are aiming at half the earthing conductor if not PME or according to the table in the regs if PME.
 
investigated a little bit more today and noticed a piece of metal connected externally to the incoming head which was bolted to some copper earth tape going up into the cabinet. The earth tape has a sticker on advising “Earthing Terminal PMS System”

Still couldn’t decipher what size the incoming conductors are as the cabinet is sealed. The armoured feeding the incoming head doesn’t have any conductor sizes marked on it.
 

Reply to Bonding Size for Old Incoming Supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
543
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
401
We have a 5.5kW incoming supply, which cannot practicably be upgraded due to our remote location in the mountains. Can I use a PV array and...
Replies
1
Views
446
Hi, searched but still niggling problem need help on... Installation: - 4mm earth to earthing electrode (rod) Ra 42ohm Zdb 33ohm 1361 60A main...
Replies
19
Views
3K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock