Search for tools and product advice,

Discuss Borrowing cpc from local socket for lighting joint box in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
73
Wonder what’s peoples thoughts on this, upstairs lighting has no cpc throughout, 2 bedrooms on ground floor on same circuit have cpcs. Cables are wired using joint box method, Found joint box for upstairs lights with cpcs cut away, reterminated this joint box but still not getting a cpc on the circuit. Must be another joint box somewhere but unable to find it as lofts been converted. Client doesn’t want the upheaval of rewiring, there’s a socket local to the joint box. Would taking a 4mm from that socket to the joint box be okay? From what I’ve read I don’t see there being an reg against it.
 
I would agree the actual circuit has no earth provided/continuity therefore it is not compliant.
IMO if the cables have earth conductors within, then borrowing cpc from another circuit is not an option, no matter how much upheaval it takes to rectify or replace.
 

Reply to Borrowing cpc from local socket for lighting joint box in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
958
Hi, I’m new to the forum. Thanks for letting me join. Asking for some diy advicd… I’m trying to add a couple more security lights to the existing...
Replies
1
Views
687
Hi all, I’ve recently had my boiler moved from the kitchen to the airing cupboard upstairs. (Changed to combi) Prior to this the hot water tank...
Replies
11
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Just want to see what people’s thoughts are on this, doing an EICR today. Testing the lighting circuit, 1 cable at every accessory which means...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock