Hi all. going to sound really thick here. adding a honeywell t6360b to a bosch greenstar 27cdi combi boiler using 3 core for the central heating only which i've done a few times. now they are wanting to add a seperate programmer and was thinking of using a honeywell st9400c. looked at the wiring diagrams and just can't figure it out.any pointers would be greatly received. do i wire the programmer from the stat or vice versa. the boiler has only one wiring point for either a stat or programmer. and looking at the programmer theres no place for a stat to wire in. i don't do much with central heating and its proberbly really simple but i've gone completely blank.
thanks to all Daz...
 
Wire the programmer from the boiler (ST10 Ls Ns E). The CH from the programmer then goes to the stat and the S/L from the stat back to Lr on ST10 in the boiler. As it's a combi you only really need a single channel programmer though.


If you find it easier, put a wiring centre in! I'd run cores for CH, HW and HW off from the progammer to the wiring centre. If using the wiring centre then you'd use:

FCU (3A) to:
1 2 3 = L N E supply
1 2 -> programmer backplate
CH on backplate -> 4
HW from backplate -> 6 (won't be used)
HW off from backplate -> 7 (won't be used)
Stat N from 2, L from 4, S/L from stat back to 5
link from 5 -> 10
boiler ST10 Lr from 10
no connections for valves.
pump is built in so no connections for that.
 

Reply to bosch combi and honeywell stat and programmer in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi there, We have recently replaced our central heating programmer with a Honeywell ST9400C. We now want to replace our old wireless room...
Replies
0
Views
741
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
Hello, I have a regular boiler doing room heating only, with a Drayton programmer (for time) + a Drayton dial stat (for temp). I've bought a...
Replies
2
Views
1K
Hi. We are looking at installing a Wiser smart heating system inc. trvs We are currently electric only, with normal rads and a Heatrae sadia...
Replies
8
Views
2K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock