Discuss Breaking capacity of a 3871 breaker? in the UK Electrical Forum area at ElectriciansForums.net

Top Cat

-
Esteemed
Arms
Reaction score
993
Anyone know what the kA of this breaker is? Also on same board i had a 30mA RCD main switch that had a BS number of 4293. Can't find that number should i just put down 61008?
 
4293 is the BS number for older type RCDs...replaced with BSEN61008....the max times are different....look in GN3 (p) 53 for rated short circuit capacity of MCBs to BS3871
 
pt1 may mean type 1, equiv. to type B in 60898.
 
Started to put details in computer package:- Cooker-type of wiring A - Ref method 100 - Points served 1 - Live 6.0mm E 2.5mm - Max dis time 0.4 - BS No 3871 - Type (automatically comes up N/A) - Breaking capacity 3
Operating current 30mA. Now at this point it should automatically work out the Max Zs. But no it comes up as "Invalid combination"!!!!!!!!!

Now have i done anything wrong or should i bypass this and put in my own figure, trouble is i can't find Zs for 3871 breakers (tables) in BGB
 
Operating current 30mA.


​should you not be entering the In of the 3871, not the RCD?
 
if it's a type 1 BS3871, the max. Zs is 230/ 4In
 
deep in the recesses of what pretends to be a brain. as a type B 60898 is 5In, type C is 10In, the 3871's type 1 is 4In, type2 is 7In. can't remember the rest.
 
Here you go...

3871 001.jpg
 

Reply to Breaking capacity of a 3871 breaker? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
867

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock