Discuss breaking capacity of fuse and mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

goldie

Cant seem to find info anywhere for bs3871 m1 plug in wylex type b mcb. Anybody know the braking capacity??
also wylex 5a fuse wire pls
Merry christmas
 
Put this into google (wiring matters 29 semi enclosed fuses )and click on the IET link that comes up
It's quicker than me writing them out
 
Cheers tel. M1 is the one i was looking for.

1ka!!??? pretty low. i guess the main incoming service fuse should cover it if pfc is high.
 
I think you will find if the CU meets EN BS 60439 the CU is rated up to 16 kA as a whole irrespective of the individual componants which vary in domestic boards !
 
I think you will find if the CU meets EN BS 60439 the CU is rated up to 16 kA as a whole irrespective of the individual componants which vary in domestic boards !

that only applies to the internal bus bars , terminals and links within the CU , it does not extend to mcb's which are rated seperately.
 
The way I understand
If the board is domestic and not exceeding 100 amp the board is covered by the suppliers fuse, the breaking capacity of the mcbs doesn't have to be greater than the PFC
Over 100 amps or non domestic the above wont apply
 
This subject has been raised a few times and I brought it up at one of the Elex Q & A sessions for that reason.

Its my beleif that the type testing on the CU is up to 16 kA.

Have a look at 530.3.4 .

And that was also the agreed answer from the panel at the Elecx show.
 
The way I understand
If the board is domestic and not exceeding 100 amp the board is covered by the suppliers fuse, the breaking capacity of the mcbs doesn't have to be greater than the PFC
Over 100 amps or non domestic the above wont apply

fuse size is irrelevent , the pfc is decided by how close the service is to the dno transformer - so even if your cut-out fuse is only 60A your pfc could be as high as 4Ka if youre 400 yrds from a local substation.
if you put 2ka fault through a 1ka mcb - it will operate but cease to work correctly from thence.
in essence , youre choosing a device that will be destroyed after tripping.
 

Reply to breaking capacity of fuse and mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
629
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
966
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I am upgrading garage lighting. I have installed 12 40W batten lights (cheap Amazon variety - don’t have specs). 6A breaker in Garage consumer...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock