Hi,

I am looking for a bit of advice on the Regs relating to BS 3036 fuses on a ring main, as I do not agree with the comments made on a PIR.

The defect states that the conductors are too small for the protective device due to the 0.725 factor.

The circuit is wired in 2.5mm2 singles in trunking/conduit. The regs state that the current carrying capacity of the ring conductors should not be less than 20 amps, which they are not. It appears that the tester has applied the 0.725 factor to the current carrying capacity which is less than 20 amps, but the regs (as far as I can tell) do not mention the application of 0.725 for this purpose.

Any comments on the situation?
 
Funny that..... As 2.5mm has been the standard cable size for ring circuits in the UK, from day one of metric cables. The early 2.5mm T&E cables also had only a 1mm CPC, now 1.5mm...

The guy's talking rubbish, ....i'd guess that probably the rest of this PIR is of the same level of competence too!! lol!!!
 
The maximum current carrying capacity of 2.5mm2 cable is about 27 amps (with the exception of a couple of cables).

If you applied the 0.725 rule to 27 you get 19.575 amps, which would also fail the 20 amp rule.
 
The maximum current carrying capacity of 2.5mm2 cable is about 27 amps (with the exception of a couple of cables).

If you applied the 0.725 rule to 27 you get 19.575 amps, which would also fail the 20 amp rule.

If the Regulations are applied literally this is true. However, the IET likes to have 'it's cake and eat it' on this one, as the OSG:2008+A1:2011 H2.3 states that an Iz of least 27A is required for A1 ring or A3 radial final circuit. Therefore 2.5mm[SUP]2[/SUP] singles, clipped direct, would meet this OSG recommendation, but in conduit or trunking will not.
 
A SIMPLE REMEDY WOULD BE TO CHANGE THE 3036 FUSES FOR 60898 PLUG IN mcbS. oops, cap lock
 

Reply to BS 3036 fuses on Ring Main. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock