UPDATE TO THE ABOVE POST:

I've found the Ze readings on the reports!

2015 report (current report) = 0.04Ω

2008 report (old report) = 0.23Ω

So... looking at the 2008 report.... 0.25 R1+R2 +0.23 Ze = 0.48 (calculated Zs). Zs per the report = 0.47. So virtually exactly the same, like you guys said. Although that might still indicate the 2008 electrician managed to get a "normal" Zs reading of some sort as the Zs figures aren't identical.

So, I think I will go back and ask the current electrician if there was a reason why he didn't use the alternative calculated Zs (ie do an R1+R2 reading) in the absence of a standard Zs reading.

Is there any issue with the differences between the two Ze readings? (the 2015 Ze reading seems quite low comparatively with the 2008 Ze reading)

This does also still leave the question about the low readings on the heating circuit insulation resistance (less than 1MΩ) so I'd be grateful if you would let me know "attention" this circuit might need, in your opinion?

Thanks guys, your help is much appreciated.

I think you are giving this spark a hard time lol.
 
Thanks Lee, just saw central heating. That said, this productt will have its own product standard to which it needs to de designed, installed, commisioned and tested.
Cheers
LOL I'm new to this - first thing I did was google the system the OP kindly provided at the outset.
The electrical installation cert for this system would be handy.
I've been taught as a tester you'd refer to previous test results as a way of monitoring changes, eg like deteriorating IR results. ETC
Seems like the OP didn't provide this info to the spark but has produced it after the inspection to question the current inspection.
Just giving my opinion, don't mean any harm to anyone.
I'm grateful to the OP cos a few years down the line when I'm competent to carry out EICRs I will hang up the phone if anyone mentions this system. LOL
 
UPDATE TO THE ABOVE POST:

I've found the Ze readings on the reports!

2015 report (current report) = 0.04Ω

2008 report (old report) = 0.23Ω

So... looking at the 2008 report.... 0.25 R1+R2 +0.23 Ze = 0.48 (calculated Zs). Zs per the report = 0.47. So virtually exactly the same, like you guys said. Although that might still indicate the 2008 electrician managed to get a "normal" Zs reading of some sort as the Zs figures aren't identical.

So, I think I will go back and ask the current electrician if there was a reason why he didn't use the alternative calculated Zs (ie do an R1+R2 reading) in the absence of a standard Zs reading.

Is there any issue with the differences between the two Ze readings? (the 2015 Ze reading seems quite low comparatively with the 2008 Ze reading)

This does also still leave the question about the low readings on the heating circuit insulation resistance (less than 1MΩ) so I'd be grateful if you would let me know "attention" this circuit might need, in your opinion?

Thanks guys, your help is much appreciated.

With regards the Ze reading differences, that is quite a difference! I have only been in business for 3 years but have not come across a Ze of 0.04Ω before, it would be interesting to know if the more experienced electricians on the site have? Even if they have then that doesn't account for the difference. Unless your area has had some electrical work done locally I may be inclined to think he has measured the Ze without disconnecting the main bonding (It would be silly to go into detail about what this actually means Soup, but you could ask him if he did).

Also, those Insulation resistance readings are far too low and you should definitely have an electrician back to check them as if they are correct then there is a fault on the circuit somewhere. I dont want to go into detail about what they mean as it just gets too confusing, also it is very difficult to say more withour being there. Your most recent electrician should have looked at this previous report.

I feel 2 hours is nowhere near enough time to do a proper electrical report on a house, unless your home is a one bedroom flat then perhaps you could justify it if it just has perhaps 3 circuit breakers in the consumer unit (fuse box). Also 2 hours could be justified if before hand you had agreed on a very specific report that was only checking certain things, but in general a report takes at least half a day (4 hours) for a 3 bed semi (I take 3/4 day for a 3 bed semi and charge £150).

I think you are giving this spark a hard time lol.

Thats what I have been thinking Lee up until Soups above 2 posts, but 2 hours to complete a full report? How long do you take Lee and be honest? :)
 
Last edited:
With regards the Ze reading differences, that is quite a difference! I have only been in business for 3 years but have not come across a Ze of 0.04Ω before, it would be interesting to know if the more experienced electricians on the site have? Even if they have then that doesn't account for the difference. Unless your area has had some electrical work done locally I may be inclined to think he has measured the Ze without disconnecting the main bonding (It would be silly to go into detail about what this actually means Soup, but you could ask him if he did).

Also, those Insulation resistance readings are far too low and you should definitely have an electrician back to check them as if they are correct then there is a fault on the circuit somewhere. I dont want to go into detail about what they mean as it just gets too confusing, also it is very difficult to say more withour being there. Your most recent electrician should have looked at this previous report.

I feel 2 hours is nowhere near enough time to do a proper electrical report on a house, unless your home is a one bedroom flat then perhaps you could justify it if it just has perhaps 3 circuit breakers in the consumer unit (fuse box). Also 2 hours could be justified if before hand you had agreed on a very specific report that was only checking certain things, but in general a report takes at least half a day (4 hours) for a 3 bed semi (I take 3/4 day for a 3 bed semi and charge £150).



Thats what I have been thinking Lee up until Soups above 2 posts, but 2 hours to complete a full report? How long do you take Lee and be honest? :)

I price it at 1/2-40 mins a circuit depending on a quick visual. TBH I hate doing EICRs....but if I do them they are done properly but most of the landlords round my way go for the cheapest quote which isn't me.
 
LOL I'm new to this - first thing I did was google the system the OP kindly provided at the outset.
The electrical installation cert for this system would be handy.
I've been taught as a tester you'd refer to previous test results as a way of monitoring changes, eg like deteriorating IR results. ETC
Seems like the OP didn't provide this info to the spark but has produced it after the inspection to question the current inspection.
Just giving my opinion, don't mean any harm to anyone.
I'm grateful to the OP cos a few years down the line when I'm competent to carry out EICRs I will hang up the phone if anyone mentions this system. LOL

Thanks for this. I've tried to get details of the system already from the management company, freeholder/freeholder's agent and the maker of the system but to no avail.

Being honest here, it completely slipped my mind that I had the 2008 inspection done until I got into the argument with the electrician about the 2015 inspection - it was fortuitous that I managed to find a copy of the report after such a long period of time! So I didn't mean to try and catch him out or anything.

With regards the Ze reading differences, that is quite a difference! I have only been in business for 3 years but have not come across a Ze of 0.04Ω before, it would be interesting to know if the more experienced electricians on the site have? Even if they have then that doesn't account for the difference. Unless your area has had some electrical work done locally I may be inclined to think he has measured the Ze without disconnecting the main bonding (It would be silly to go into detail about what this actually means Soup, but you could ask him if he did).

OK I'll ask him that and see what he says!

Also, those Insulation resistance readings are far too low and you should definitely have an electrician back to check them as if they are correct then there is a fault on the circuit somewhere. I dont want to go into detail about what they mean as it just gets too confusing, also it is very difficult to say more withour being there. Your most recent electrician should have looked at this previous report.

As noted above, he didn't have sight of this old report but that's only because he wasn't aware of it (and I wasn't reminded of it until after the inspection).

I'll ask him again about the insulation resistance although I think it'll annoy him and he'll just refer back to the fact there was no power in the circuit and/or there are pin timers in the circuit, preventing a proper test!

I feel 2 hours is nowhere near enough time to do a proper electrical report on a house, unless your home is a one bedroom flat then perhaps you could justify it if it just has perhaps 3 circuit breakers in the consumer unit (fuse box). Also 2 hours could be justified if before hand you had agreed on a very specific report that was only checking certain things, but in general a report takes at least half a day (4 hours) for a 3 bed semi (I take 3/4 day for a 3 bed semi and charge £150).

To be fair, the 2 hours was just an estimate based on his hourly rate for other non-electrical work (£45/hour) so just a guess on my part. My property is a 2-bed flat so maybe that would be OK in terms of time spent in this instance. The fact he didn't measure certain things like R1+R2/R2 etc might be where he "saved time". Nice to know my continual questions don't seem to be so over the top now though :shades_smile:
 
[FONT=&quot]Wishing every success with your venture Soup – there seems to be endless red-tape with absolutely everything these days. [/FONT]
 
I'll ask him again about the insulation resistance although I think it'll annoy him and he'll just refer back to the fact there was no power in the circuit and/or there are pin timers in the circuit, preventing a proper test!

Sorry to leap in late, but I've read this whole thread and I'm puzzled about something. Why would a lack of power affect insulation resistance tests? They have to be done with the power off. Zs testing can be done by measurement or calculation, meaning that, if you do a measured Ze test, you can calculate by adding R1 and R2, or you can measure Zs wit the power on. However IR testing is definitively a dead test.
 
Would doing a Ze test with all the EARTHS in give you a real Dam Low 0.04Ohms value, apose to the 0.23 Ohms the last time

As YoungScud (so wanted to type in YoungStud then) said IR is a DEAD test, so No power Great, Zs a Live Test other wise its the R1+R2+Ze=Zs with no Power would be yes.
 
Would doing a Ze test with all the EARTHS in give you a real Dam Low 0.04Ohms value, apose to the 0.23 Ohms the last time

As YoungScud (so wanted to type in YoungStud then) said IR is a DEAD test, so No power Great, Zs a Live Test other wise its the R1+R2+Ze=Zs with no Power would be yes.


Leaving the parallel paths in circuit might or might not significantly affect the reading (the more parallel paths, the more likely the difference will be large). It's the whole reason that Ze measurements should be done with the customer's bonding conductors disconnected, and consequently the installation switched off.

By the way, YoundStud is Ok with me. That gives me an idea...
 
It was more of me suggesting that they really do a Zs/Zdb reading and why the 0.04ohms for Ze

With more points to Earth the resistance will drop (ie parallel Resisters)
 
Right then gents, got another response in this continuing saga.

Regarding his inability to read the Zs on the heating circuit and the off-peak immersion, I asked the following question:

"regarding the Zs reading, it seems you can "calculate" the Zs using the R1+R2 and Ze readings as an alternative in certain circumstances (eg if the power is off, like in our case). Maybe that's how the previous electrician calculated the Zs for both the off-peak immersion circuit and the heating circuit on the 2008 report? (although I note the 2008 figures don't quite match using this calculation, they are very close)."

His response :

"Yes, indeed it can be done this way, but then you have to measure the values of r1 and r2 which as I mentioned before, this continuity testing was not done in this case as you have to actually have continuity without switches or timers in the way. I can’t comment on how the 2008 test was done."

My 2nd question was:

"Just out of interest, having now had sight of the 2008 periodic inspection report, is there anything you noticed from the comparative figures that you think I should be aware of? ie are there any notable differences in the figures between the two tests that points towards degradation of any sort, potential problems now or in the future etc- eg Ze figure of 0.04Ω in 2015 vs 0.23Ω in 2008; also, cooker Zs jumped from 0.23 in 2008 to 1.2 in 2015, the latter figure being above the maximum permitted Zs figure of 0.85 noted on the 2008 report."

His reply was :

"This is getting a bit vague as it was a while ago now, but this value was probably obtained from the socket on the side of the cooker switch rather than the cooker circuit on its own, hence the higher value reading."

So... any thoughts on his comments on either of these? Does the point about switches/timers affecting continuity make sense?

He hasn't really answered the Ze point on my 2nd question, nor has he commented whether the Zs value on the cooker is overly high/outside of the maximum permitted figure of 0.85 per the 2008 report either (NB the cooker is "hard-wired" rather than having a 3-pin plug).
 
Overall you have had an EICR done on the property, you have been supplied with the appropriate paperwork.
The electrician has failed to cover one aspect of the inspection, which you had specifically asked about, and his response about this was that it was outside his expertise to do this.
You are then querying further aspects of his work (which are somewhat odd but likely he was pushed for time and could not cover all the additional slow testing) and have now produced a report that could have saved him a significant amount of time and you some money and are now querying the comparisons which he had no opportunity to make.

I do not think you are going to be successful in getting any further work from this electrician as it will seem as if there is nothing he can say that will bring this to a close.
 
Overall you have had an EICR done on the property, you have been supplied with the appropriate paperwork.
The electrician has failed to cover one aspect of the inspection, which you had specifically asked about, and his response about this was that it was outside his expertise to do this.
You are then querying further aspects of his work (which are somewhat odd but likely he was pushed for time and could not cover all the additional slow testing) and have now produced a report that could have saved him a significant amount of time and you some money and are now querying the comparisons which he had no opportunity to make.

I do not think you are going to be successful in getting any further work from this electrician as it will seem as if there is nothing he can say that will bring this to a close.

Thanks for taking the time to reply, but I think you're missing the point here a little.

The previous report - which I was only reminded of after the recent test because I was querying why he hadn't completed testing on certain circuits - was only sent to him to ask him how the previous electrician may have managed to get readings where he couldn't (I know I have since asked him to compare the figures on the report but my reasoning for this is set out below).

At the end of the day, as a landlord I need to be able to say that the internal electrics of the property are safe. The previous report had more detail generally, as well as completed readings for the tests he was unable to complete - and this coupled with the fact that there is further doubt about the reliability of some of his readings/methods (even you say that some aspects of his work are "odd" in your post), makes we wonder whether his report as a whole can actually be relied upon. Hence my questions to the good people of this board, and further questions to the electrician, to try and understand it all a bit more and ascertain whether this is the case - which I'm well within my rights to do.

Put simply, I don't see why I should pay for a job if it has not been done properly (if indeed this is the case here). And to be honest, I'm still unsure what the true situation is! :rolleyes4: And even if I do ultimately get a resolution I'm unsure if I would use this electrician again anyway, given the protracted nature of the post-report discussions I've had with him.

And finally, just an FYI - I am being charged a flat fee for the work, so no extra costs for time spent as far as I am aware.
 
I think you have raised an interesting point with us, you are unhappy to pay for a report that is unreliable, however you have not raised this point with the electrician, you have only kept asking him further questions of a specific nature.
I would suggest that if you are unhappy with the report that you inform the electrician, as you have just done here, of your reasoning and see what comes of that.
We are unable from a distance to be able to specifically state if something is definitively wrong; there are some "odd" items but these may be due to various circumstances that we are unaware of as we only have the information you have given us..
 
I think you have raised an interesting point with us, you are unhappy to pay for a report that is unreliable, however you have not raised this point with the electrician, you have only kept asking him further questions of a specific nature.
I would suggest that if you are unhappy with the report that you inform the electrician, as you have just done here, of your reasoning and see what comes of that.
We are unable from a distance to be able to specifically state if something is definitively wrong; there are some "odd" items but these may be due to various circumstances that we are unaware of as we only have the information you have given us..

I have already told the electrician I was unhappy he didn't/was unable to test certain circuits that I had specifically asked him to ensure were looked at, prior to starting the report.

However, like I said in my previous post, I'm still unsure if the report is unreliable, or if he has actually done anything wrong which warrants me complaining further. There are a lot of "question marks" here, but at the end of the day it wouldn't be right for me to make baseless or ill-informed accusations at him if he's done his job properly. Hence my continued questions on here trying to get to the bottom of it all!

I do understand your point about being unable to specifically state if something is definitively wrong "from a distance", as you put it. I was aware this was unlikely to be a straightforward black and white problem and the responses to date have indicated that. However, IF there was something in the information I had provided that you guys highlighted which was clearly incorrect/wrong then I could query him on it - and this is what I was trying to ascertain in my last set of queries.

Hope that clears it up!
 
Last edited by a moderator:
The Ze, I think 0.04 is dam low, you living next door to a sub station.
As for the value can be got by measure or just asking, don't think the board will give a value that meets.thenbs7671 standards for your setup

R1+R2, could I guess link at db (turning off power to this) and doing a.R1+R2 To the accom7 and then link at the accom7 then to the heater
Zs = Ze + (R1 + R2 [Db to accom7]) + (R1 + R2[accom7 to heater])

This may get edit because saying some thing shouldn't do, but R1 is about the same value as Rn and the circuit works, so I know R1 is good
So would doing Zs = Ze + Rn + R2 be about the same as Zs = Ze + R1 + R2
It will prove continuity for R2 and Rn, and we know R1 works as the heater works
Insulation Resistance test too
 

Reply to BS7671 test and internal electric heating in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I am seeking a job as an electricians mate / improver / labourer around South Yorkshire. I am based in Doncaster, i have a uk full driving licence...
Replies
3
Views
505
Firstly, thank you for taking the time to read this. I am not trained in electrics whatsoever, I am a just a home owner looking for advice. I...
Replies
2
Views
970
  • Locked
Required asap for price work. No of Workers: 2 Location: Brighton & Hove Description of Work: Installation of 230v operated, radio linked smoke...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock