Update: Freddo has been very busy but managed to attend the sports ground with the defective swa cable last weekend. We had some conversations on my test rig and how to use it in the private area which I have copied below:

testfreddo.jpg


Good morning. A 25mm2 conductor has a resistance of 0.000727 Ohms/m. When a current of circa 75A flows through it the voltage drop is 75 x 0.000727 = 0.055V/m. Not much. A 40m length of 25mm2 conductor will drop a voltage of 40 x 0.055 = 2.2V Thus when you measure the near and far voltages with your dvm you will need to drop down in range scale in order to obtain the necessary resolution. My dvm has a 2000mV range which would be ideal for example.

We are using a variation of the 4 wire resistance measurement method. It is important that the 'voltage sense' connections are on the 'outside' of the near and far current loop connections. See para 2 of :

4 Wire Testing | Resistance Measurement to within 1mΩ | How-To - https://www.camiresearch.com/Campaigns/Web-Articles/4-wire-testing.html

So at the far end the Henley is wired with the middle terminal to black and right to red - the current loop - and the sense connection blue is made to the left of the black to the middle terminal.

A nice feature of this set up is that the near readings will be negative voltages and the far ones positive due to the negative terminal of the dvm being connected to the point of fault. You should see this when you do the on arrival survival tests with the three 3.3R test resistors.

After measuring R-Y, I recommend you swap the SWA for the Yellow and take the R-SWA measurement. Finally swap the Yellow for the Red and take the Y-SWA measurement.

You need to know the length of the cable in order to use the data to divide it into near and far. Say Near is 250mV Far is 1850mV Distance to fault from start of cable is length of cable x 250/(250 + 1850). My example in the image indicates the cable is damaged only in one place. The most likely region is as I have shown.

When I have the voltage measurements I will do the sums.
 

Attachments

  • swafreddoRY.png
    74.5 KB · Views: 4
  • scatter plot.png
    45.5 KB · Views: 3
  • scatter plot 2.png
    13.4 KB · Views: 2

Reply to Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
529
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
294

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock