Discuss Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi all,

My first post here, thought I'd see if it was possible to get some advice or tips...

Basically, I had a large amount of block paving and large concrete base laid at the far end (25m) of my garden a few months ago. Under this I had 3 core 16mm SWA laid.

(I most definitely can't vouch for the quality of the work done by any of these guys)

More recently me and my brother built a large garage on the concrete base and had an electrician add a new CU in the garage and connect the other end of the SWA to an MCB in the CU in the house.

Today, after about 2 weeks of not having any problems, the RCD in the house tripped out and wouldn't switch back on unless I turned off the MCB to the garage. It's worth noting, it rained fairly heavily last night.

After trying a few different things, I've eventually disconnected the SWA from the CUs at both ends.

I've tested for continuity across all cable/ armour combinations and noticed there's continuity (beeping) when I touch the live and armour.

Is my assumption that someone has damaged the cable, breaking the live wire insulation and water has entered this and created a circuit between the live and the armour a reasonable one? Are there any other ways this continuity could occur given both ends are now fully disconnected?

Assuming this assumption is correct, I'm curious if there's a simple way for me to locate this fault without digging up 30m of block paving?

For example, I was wondering if, by using a multimeter and testing the resistance across the live and armour at both ends I might be able to work out how far down the wire the break is?

So maybe if I got a resistance 10 times higher at one end than the other I can assume the damage to the 25m long cable is 10% (2.5m) from the end of the cable with lower reading?

I guess I don't need to be super accurate and that there are industrial tools that could accurately locate the fault, all I really want to know is roughly were to start digging in the hope of keeping the damage to the paving to a minimum.

Thanks in advance for any help or suggestions.

Dan
 
Yes, a difference in resistance measured from each end should give you a rough place to start digging
 
What were all the readings between cores and between cores and armour?
and end to end continuity of each core?

as it’s a 3 core, you could swap the colours and use the shorting out core as earth.

That’s only possible if only one core is damaged. And it’s not a long term solution as any moisture will eventually rot the armour away.
 
if the resistance is low enough to cause a multimeter to beep, then it's not water ingress. youneed accurate readings between each core and armour.luckily itmayonly be 1 core affected so littlespark's idea of a temp. fix could be a winner.
 
Even if you work out how far from each end it is, and unless you know for sure it’s in a straight line and not wiggling all over the place…. You might still end up digging a 6ft wide hole looking for it.

Advise getting a professional with proper test equipment to check it. Your multimeter may not be picking up slight damage to a second core which would scupper my suggestion above.

multimeters give out roughly 9v…. Professional gear- up to 1000v
 
What were all the readings between cores and between cores and armour?
and end to end continuity of each core?

as it’s a 3 core, you could swap the colours and use the shorting out core as earth.

That’s only possible if only one core is damaged. And it’s not a long term solution as any moisture will eventually rot the armour away.

If the cable has been damaged enough to short a core to the armour then surely it needs digging up and a repair made to it.
 
This is one of those situations where I'd have installed the cable in a duct. So many times I've come across this where the cable is installed under ground that has been landscaped or an hard standing added.
a vote in favour of putting it in ducting, methinks.
I was just writing a post stating exactly this! :-

In my experience a cable laid underground that will become inaccessible (under hard finished surfaces) should be ducted. This solves a couple of problems (provide the duct doesn't get damaged and is installed correctly) 1. if the cable gets damaged it can be drawn out and replaced. 2. If the building that is being supplied requires a supply upgrade either an additional cable can be added, or the original drawn and replaced.
 
The OP has the right idea about measuring resistances from each end. Most of the expense is finding these faults. A left of field suggestion would be to acquire an insulation resistance (IR) tester, eBay always has lots of them as sparks ditch their separate testers and get all in one units. A megger bm403 or similar would be fairly cheap and very helpful in this situation.
 
New posts

Reply to Buried SWA cable fault finding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
596
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
851
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
353

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock