Cable calcs 3 phase

Discuss Cable calcs 3 phase in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Its been long since I was in college doing cable calcs and obeing onsite as I've studied a completely different course at university, I understand de-rating factors but need some clarifying up to brush up.

If I need a 600A supply which can be split 200A each phase. and being supplied via SWA underground over a distance of 200m at a depth of 0.8 to a sub dis board.

When doing cable calcs do I use 200A or 600A?
And when reading cable datasheets for 3 phase reference method d - 1|thee or 1 four-core cable three-phase AC , does the data in the table refer to each phase ie. as 1mm2 - 21A per phase or 7A.
Bit of a stupid question

Thanks for your help.
 
Another thing to consider is the voltage drop over 200m.
 
Hi - there are no stupid questions, but my thought is you should be able to work this one out from first principles. Have you got BS7671 to hand? In your example what is single phase current carrying capacity for 1mm? Then for 3 phases at 1mm?
 
Cable calculations and data tables are based on the actual current in each conductor. You happen to have single-phase loads spread over the three phases of a 200A 3-phase, 4-wire circuit. If instead you chose to supply the loads from a single-phase circuit, the conductor current would then be 600A and that would be the figure to use in the calculations.
 
Cable calculations and data tables are based on the actual current in each conductor. You happen to have single-phase loads spread over the three phases of a 200A 3-phase, 4-wire circuit. If instead you chose to supply the loads from a single-phase circuit, the conductor current would then be 600A and that would be the figure to use in the calculations.
Thanks , think i just had a brain meltdown yesterday
 

Reply to Cable calcs 3 phase in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock