- Reaction score
- 5,607
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and bonding a bit later or on another thread!
We have a 3 phase supply (100A p/phase). From supply to first barn (we'll call it Barn A) is 70 metres. For example purposes lets say this is 35mm (5 core) leading to a 3 phase board.
In Barn A there will be 4 x temporary offices (1 - 3 years) each with a 32A single phase supply (2 x double sockets, 1 x light, 1 x 3kW heater in each office). There will also be 2 x single phase (7kW) EVCP. Also a 16A (3 phase) commando socket (being used to supply a a charger for an electric tractor, unsure of kW)
From Barn A out to the poly tunnels it will be a 140meter run. I am assuming a max demand at the poly tunnels of 32A. I do not have exact figures yet. For example purposes lets say this is 25mm (3 core)
Lets say it's all in SWA (70°c, table 4D4A).
Working backwards we have a VD between Barn A and polytunnels of (140m x 32A x 1.75) / 1000 = 7.84v
VD between Supply and barn A (assuming no diversity) = (237A x 70m x 1.1) / 10000 = 18.25v
Clearly the voltage drop is too great (26.09V)
Some questions I have are..
1. Is the maths right?
2. Where could I apply diversity in order to avoid using excessively large cables?
3. What is an acceptable VD for 3 phase (is it 4%)?
4. The supply is approx 100m from the transformer so actual voltage will be higher than design voltage of 400V. Can we utilise actual voltage or should we always use design voltage?
5. The polytunnels are actually only 50m from the transformer, could it be a feasible idea to get DNO to fit separate supply for this? This would avoid the long run of cable.
We have a 3 phase supply (100A p/phase). From supply to first barn (we'll call it Barn A) is 70 metres. For example purposes lets say this is 35mm (5 core) leading to a 3 phase board.
In Barn A there will be 4 x temporary offices (1 - 3 years) each with a 32A single phase supply (2 x double sockets, 1 x light, 1 x 3kW heater in each office). There will also be 2 x single phase (7kW) EVCP. Also a 16A (3 phase) commando socket (being used to supply a a charger for an electric tractor, unsure of kW)
From Barn A out to the poly tunnels it will be a 140meter run. I am assuming a max demand at the poly tunnels of 32A. I do not have exact figures yet. For example purposes lets say this is 25mm (3 core)
Lets say it's all in SWA (70°c, table 4D4A).
Working backwards we have a VD between Barn A and polytunnels of (140m x 32A x 1.75) / 1000 = 7.84v
VD between Supply and barn A (assuming no diversity) = (237A x 70m x 1.1) / 10000 = 18.25v
Clearly the voltage drop is too great (26.09V)
Some questions I have are..
1. Is the maths right?
2. Where could I apply diversity in order to avoid using excessively large cables?
3. What is an acceptable VD for 3 phase (is it 4%)?
4. The supply is approx 100m from the transformer so actual voltage will be higher than design voltage of 400V. Can we utilise actual voltage or should we always use design voltage?
5. The polytunnels are actually only 50m from the transformer, could it be a feasible idea to get DNO to fit separate supply for this? This would avoid the long run of cable.
Last edited: