Currently reading:
cable calculations single phase / 2 phase

Discuss cable calculations single phase / 2 phase in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hello all

Just doing some cable calcs for a shepards hut site, the site has an incoming supply of 2 x 250a single phase supplys, was hoping to run a 4 core down from incomer to a board then split off to each hut.

Do i have to work it out on single phase 230v or can i work it out on 400v
 
Single phase/2 phase, commonly known as split phase is 230 - 0 - 230 volts, with the two phases 180 degree apart. Not the same as using 2 phases of a three phase supply, where the phases are 120 degrees apart.
If there are no loads which run off of the 400V (or 460V) supply, then as above, calculations are for the worst case scenario, where all the load is on one phase.
 
Single phase/2 phase, commonly known as split phase is 230 - 0 - 230 volts, with the two phases 180 degree apart. Not the same as using 2 phases of a three phase supply, where the phases are 120 degrees apart.
If there are no loads which run off of the 400V (or 460V) supply, then as above, calculations are for the worst case scenario, where all the load is on one phase.
Cheers

theres no 3 phase on site just the split phase

il work it out on single phase am i ok working it out on saying if its a 200a total supply i can do 100a on each phase and use same cable
 
So it is 460V across phases?
The size of the neutral will need to be calculated for the maximum load on the phase which has the highest calculated max load. This is the worst case scenario.
When a load is applied to the other phase, the current in the neutral will decrease, as will the total voltage drop.
If both phases are drawing the same load, the current in the neutral will be zero, and the voltage drop will be half of that when just one phase is loaded.
 

Reply to cable calculations single phase / 2 phase in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock