Discuss cable calculations single phase / 2 phase in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hello all

Just doing some cable calcs for a shepards hut site, the site has an incoming supply of 2 x 250a single phase supplys, was hoping to run a 4 core down from incomer to a board then split off to each hut.

Do i have to work it out on single phase 230v or can i work it out on 400v
 
single phase calcs.
even if you are sharing the N you could be in a situation where all the load is on one hut and none on the other.
 
Single phase/2 phase, commonly known as split phase is 230 - 0 - 230 volts, with the two phases 180 degree apart. Not the same as using 2 phases of a three phase supply, where the phases are 120 degrees apart.
If there are no loads which run off of the 400V (or 460V) supply, then as above, calculations are for the worst case scenario, where all the load is on one phase.
 
Single phase/2 phase, commonly known as split phase is 230 - 0 - 230 volts, with the two phases 180 degree apart. Not the same as using 2 phases of a three phase supply, where the phases are 120 degrees apart.
If there are no loads which run off of the 400V (or 460V) supply, then as above, calculations are for the worst case scenario, where all the load is on one phase.
Cheers

theres no 3 phase on site just the split phase

il work it out on single phase am i ok working it out on saying if its a 200a total supply i can do 100a on each phase and use same cable
 
So it is 460V across phases?
The size of the neutral will need to be calculated for the maximum load on the phase which has the highest calculated max load. This is the worst case scenario.
When a load is applied to the other phase, the current in the neutral will decrease, as will the total voltage drop.
If both phases are drawing the same load, the current in the neutral will be zero, and the voltage drop will be half of that when just one phase is loaded.
 

Reply to cable calculations single phase / 2 phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
923
Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
665
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
546
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock