Search the forum,

Discuss Cable Current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

T

Tonkolili

Why is it that the tables in the Regs for Cable current carrying capacities vary so much from that of a cable manufacturers data sheet, for example a table in the Regs book states a 240mm 4 core XLPE Armoured cable buried will carry 324 amps, but a data sheet for a leading manufacturer states 516 amps.
 
Are you sure the temp ratings are the same?
 
The regs are British Standards and work on the worse case scenario as the tolerances of cables varies greatly dependent upon the make-up of the sheath/insulation.

You can use the manufacturers guide but caution that the tables they state are compliant to the UK regulation and not say reflecting a CCC for a country who's requirements are more relaxed this is where ambient ground and air temp's may give a different outcome.

The table you used is specifically for -

Air ambient at 30 degrees.
Ground ambient 20 degrees.
Conductor operating temp' 90 degrees.

The table you are using is not commonly used as most equipment you'll connect to will only have a 70c rating meaning you need to use table 4D4A instead.

Lastly the table you are referring from also has ducted swa which reduces the effective heat dissipation so its really ignoring direct buried cables for the worse case ducted ones.
 
Last edited:
Just checked this out myself.
Eland cable XLPE/PVC/SWA/PVC 240mm Direct In Ground is 324A.
Anixter XLPE/PVC/SWA/PVC 240mm Direct Burial is 529A.
 
Why is it that the tables in the Regs for Cable current carrying capacities vary so much from that of a cable manufacturers data sheet, for example a table in the Regs book states a 240mm 4 core XLPE Armoured cable buried will carry 324 amps, but a data sheet for a leading manufacturer states 516 amps.
It depends on installation method which affects the ability of the cable to dissipate heat.
Direct burial is like thermal insulation compared to being mounted in free air or on perforated tray.
 

Reply to Cable Current carrying capacity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
331
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
995
Hi Doncaster EV ultra cable: Does anyone know what the current capacity of these cables is given particular reference methods? The spec sheet...
Replies
3
Views
2K
Hi Guys Any one know the current carrying capacity of a 4mm 3 core single phase sy cable ran in a 20mm pvc conduit? Not sure of the right table...
Replies
2
Views
959
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top