The owner has had a 'lean to' build of bricks/blocks and wants a couple of sockets and a light installed.
There is a supply, to the existing detached garage which is due for removal, and I can use its way in the CU for the above.
There are no extraneous conductive parts in the new (permanent) build. The new build is accessible from outside i.e. no access from within the house. Also the CU is adjacent to the new build so easily connected as if in the next room.
The cable, in effect, will not be external at any time as the new build has been keyed into the side of the house at each end and lead flashing fitted along the adjoining wall/roof.

Having not met this scenario before, my preferred method is to run t&e through the wall (at a suitable angle down) to the new build. Fit a double pole isolator and a fcu for the light.
If the new build was detached swa would be my choice. However, ...

My questions are:
Do I have to utilise swa to the new build? or will t&e do?
Does there need to be an isolator in the new build? (or a CU?) Obviously a CU will pump the price up.

Please ask if more information is required.
Thanks for your time.
 
Thanks Archy,
The owner doesn't want pvc conduit! Clipped direct is his choice.
RCD protection is in place.
I installed their bonding, so that's okay.
 
what is your training?
Boydy



Ronald-McDonald-6.gif

?

B-)
 
Thanks Archy,
The owner doesn't want pvc conduit! Clipped direct is his choice.

I think 20mm conduit is about £1 a length + Vat. For the sake of a fiver I think i'dbe piping it ;)

Your the electrician at the end of the day. Do you think its acceptable to clip direct into switches/sockets? (Because I certainly wouldn't!!)

Rich
 
I think 20mm conduit is about £1 a length + Vat. For the sake of a fiver I think i'dbe piping it ;)

Your the electrician at the end of the day. Do you think its acceptable to clip direct into switches/sockets? (Because I certainly wouldn't!!)

Rich


Generally if the finished job looks like crap, it normally is Crap!!
 
nowt wrong with surface T/E and enclose the drops in mini trunking or pvc tube.
 
nowt wrong with surface T/E and enclose the drops in mini trunking or pvc tube.

Think that's what were saying, although mini trunking looks naff at the best of times. Looks a much better job all round in a nice bit of PVC tubing. It will also provide a degree of mechanical protection into the surface installation too!!
 
Think that's what were saying, although mini trunking looks naff at the best of times. Looks a much better job all round in a nice bit of PVC tubing. It will also provide a degree of mechanical protection into the surface installation too!!

Have you been out in the sun too much?
 
although the best way by far, steel conduit is a bit of overkill in uncle joe's domestic garage, though.
 

Reply to Cable requirement for attached workshop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
570
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
820
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
774
Hi all. Looking to buy a house where the rear of the house is the rear boundary, onto council owned land (a footpath). I want to build a new...
Replies
4
Views
1K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock